Remote Compressor Start
I am half way through a (very) long build of a second shed. I plan to link the 2 sheds with a sally port of sorts and put the compressor and air dryer in there. Both are 3 phase (currently also changing the consumer mains from single to 3 phase).
I want to have separate on/off switches for the compressor and dryer located at the entry to the sheds so that I can turn them on and off remotely. I will purchase one of the switches that BobL linked to earlier today but what is the other component I need? Some sort of a 3 phase relay? The compressor is only 13CFM but I intend to upsize if $ ever becomes available. I don't have a clue what the dryer draws but I presume much less than a compressor.
I don't want to use a huge length of expensive orange circ to the switches but would rather use some low current (= cheaper) stuff.
-
14th Jul 2022, 07:17 PM #2Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Compressors over about 2HP are best started using a contactor in between those cheap switches and the compressor.
Your 3P compressor will almost certainly already have a 3P contractor - you will have to figure out if it can be remotely switched.
I turn my compressor on/off using it's breaker when I enter/leave my shed.
-
14th Jul 2022, 10:40 PM #3Most Valued Member
- Join Date
- Mar 2011
- Location
- Southern Flinders Ranges
- Posts
- 1,554
Use contractors with 24V DC coils instead of AC, the only AC cable required then is from the sub board to the control box. Not an overly difficult proposition for a man of your talents.
-
14th Jul 2022, 11:41 PM #4Golden Member
- Join Date
- Apr 2019
- Location
- Adelaide
- Posts
- 596
What Mr Tadpole described is exactly what I had in mind.
So something along these lines? https://www.sparkydirect.com.au/p/CA...kw-1n-o-a.html
-
15th Jul 2022, 05:38 AM #5Most Valued Member
- Join Date
- Nov 2007
- Location
- melbourne australia
- Posts
- 3,228
That one has a 240V coil. RT suggested a 24V coil. It doesn't look like they have a 3 pole contactor with a 24V coil.
Chris
-
15th Jul 2022, 05:40 AM #6Most Valued Member
- Join Date
- Nov 2007
- Location
- melbourne australia
- Posts
- 3,228
-
15th Jul 2022, 08:50 AM #7Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
-
15th Jul 2022, 11:28 AM #8Most Valued Member
- Join Date
- Mar 2011
- Location
- Southern Flinders Ranges
- Posts
- 1,554
Just be careful which flavour of 24V coil you purchase, they are available in both AC and DC. Supply needs to match the coil.
Sparkydirect may not stock 24V DC but they are readily available
https://au.rs-online.com/web/p/contactors/4930163
Simplest and cheapest way to get control voltage is a DIN rail power supply, just about every electrical place has them and they are relatively cheap.
-
15th Jul 2022, 12:24 PM #9Senior Member
- Join Date
- Apr 2018
- Location
- Perth
- Posts
- 168
-
15th Jul 2022, 03:10 PM #10Most Valued Member
- Join Date
- Mar 2011
- Location
- Southern Flinders Ranges
- Posts
- 1,554
Yah, 24VAC is certainly an option, I just tend to think in DC for control because that’s what we use at work.
-
15th Jul 2022, 05:17 PM #11Golden Member
- Join Date
- Apr 2019
- Location
- Adelaide
- Posts
- 596
is there something wrong with using a 240v control circuit? No need for any additional bits and I would assume small size wire could be used?
-
15th Jul 2022, 05:58 PM #12Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
-
15th Jul 2022, 07:38 PM #13Most Valued Member
- Join Date
- Mar 2011
- Location
- Southern Flinders Ranges
- Posts
- 1,554
-
15th Jul 2022, 07:44 PM #14Diamond Member
- Join Date
- Aug 2019
- Location
- Revesby - Sydney Australia
- Age
- 57
- Posts
- 1,195
Low voltage trigger is safer, and it means you don't need to worry about having the same 240v circuit in both sheds.
By "same circuit", I mean you need the same active neutral pair, on the same safety switch (RCD/RCBO). These days, I think the neutral probably also needs to be bonded to earth in all locations. See https://memberarea.necawa.asn.au/Adm...d-neutrals-men
Low voltage could be a local 24V plug pack in each shed, with tiny little figure 8 cable to the compressor contactor, and two diodes so that the output of one plug pack doesn't drive the other one if you have both switches on.
If you can't find an appropriate contactor, a 3phase SSR can do the same thing:
https://fastron.com.au/collections/3...cts/fth2553zd3
Just mount it on a heatsink if your compressor is large.
You could even control it with a switch and 9V battery in both sheds - the ultimate in wiring safety and simplicity?
-
15th Jul 2022, 10:04 PM #15Senior Member
- Join Date
- Jun 2016
- Location
- Sydney
- Posts
- 283
Mill motor
My mill has a 3-phase motor.
The supplied 3-pole switch was wonky and had to be replaced.
I did not like any of the readily-available 3-phase switches: either flimsy or overkill.
So
I pull a single phase off the supply to a standard architrave wall (lighting) switch.
That drives a 240 VAC coil on a heavy 3-phase contactor stuck inside the mill body. Sprecher& Schuh.
To be sure, when I switch the mill on you can hear the contactor pull in, with a clunk.
The contactor is rated for motors, with a starting surge.
The system works fine, and has done so for many years.
Cheers
Roger
Similar Threads
-
VFD Remote Switch Panel
By danshell in forum ELECTRICALSReplies: 34Last Post: 23rd Sep 2020, 11:08 AM -
Vfd remote switches.
By eskimo in forum ELECTRICALSReplies: 9Last Post: 8th Jun 2019, 11:22 AM -
Remote control of the HUANYANG VFD
By morrisman in forum METALWORK GENERALReplies: 17Last Post: 16th Feb 2015, 07:31 AM -
VFD Remote Cable
By Oldneweng in forum METALWORK GENERALReplies: 18Last Post: 14th May 2014, 07:39 AM -
OT: Compressor won't start. Cap or ?
By Bryan in forum METALWORK GENERALReplies: 7Last Post: 26th Jul 2011, 11:28 PM