    im having trouble with the 1 hp motor tripping the vfd( huanyang 1.5 kw) when only using light loads on my lathe.
    it appears that its an over current fault ( set at 1.76) it shuts down when the vfd shows about 2,2 amps
    i have read in the cnc forums that they set the motor current to maximum ( 7 amps) is this advisable
    john
    Last edited by tanii51; 27th Jul 2011 at 01:08 PM. Reason: typos

  2. #2
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    Hi John,
    Is this at 50Hz? I have this sort of problem when I get down under about 15Hz.
    (not much help I know but the answer may help others give you an answer)

    Stuart

  3. #3
    Join Date
    Nov 2005
    Location
    adelaide
    Posts
    597

    Default

    thanks stu i just did a kill it or fix it experiment i cranked the amps in the parameters up to 5 and then watched how high the reading would go turning a piece of caste on slowest back gear but realy making it work; it got to about 3 the motor wasnt getting hot evrything seems ok so maybe that all it needs ( perhaps set it at 4 just to be on the safe side )
    john

  4. #4
    Join Date
    May 2010
    Location
    Lower Lakes SA
    Age
    58
    Posts
    2,607

    Default

    What's the amperage value on the motor? You're supposed to enter this value as max current.

  5. #5
    Join Date
    Nov 2005
    Location
    adelaide
    Posts
    597

    Default

    bryan the motor plate says 1.76 amps (.75 kw) this is the second motor i have tried and both shut the vfd down on only light cuts when the amps as indicated on the motor plate are entered .it usually shuts down around the 2.2 amps .
    for a motor this size i should be able to take much deeper cuts on the slow speed ( i have 2 other hercus lathes with single phase motors to compare it against )
    as i said in the last post upping the amps to 4 seems to have solved the problem, i got this suggestion fronm the cnc forum where the same vfd is used on cnc spindles ( they program in 7 amps )
    but welcome all suggestions
    john

  6. #6
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    5,080

    Default

    Hi John,

    The 7 amps would be for 1.5Kw motors. At the front of the manual they have a table of inverter models that lists motor size and inverter capacity

    (I tried to insert the table but didn't work...) Lets try a jpeg...



    I don't think that the 3 or 4 amp current limit will damage your motor, certainly won't hurt the VFD.

    That said, Brian is correct, the normal procedure is to use the motor nameplate current, but that assumes 50Hz...

    Regards
    Ray

Similar Threads

  1. Single Phase Motor Question
    By Glenhuon in forum METALWORK GENERAL
    Replies: 3
    Last Post: 22nd Oct 2009, 10:49 AM
  2. Replies: 24
    Last Post: 27th Feb 2007, 05:24 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •