    Default Single phase input VFD to 3ph output on a lathe

    Hi, I've just connected a new VFD to the 3ph 415v 2 speed motor of my lathe. Problem; The motor will now run up to full speed (2800) no problem, BUT only after I give the pully an initial push start. The VFD is a Nflixin single phase 240v input to 3ph 380v output. I've changed a few parameters in settings, eg. speed to 2800, acceleration time to 5 seconds, volts to 415 but nothing else. Motor is around 50 years old but seems to run very nicely once going.
    Thanks
    woodworm.

  2. #2
    Join Date
    Aug 2021
    Location
    Sydney
    Age
    46
    Posts
    117

    Default

    Maybe it dosen’t like too much variance from the 50Hz it was designed for?

    Unsure though as most people seem to rave on about how much range of speeds they can get from a vfd

  3. #3
    Join Date
    Jul 2006
    Location
    Athelstone, SA 5076
    Posts
    4,258

    Default

    are you sure you have 415v across all three phases at the motor terminals?

    are you saying the motor is a 2 speed motor? and you have tried to configure accordingly to work from the VFD on both speeds?

  4. #4
    Join Date
    Sep 2008
    Location
    Riddells Creek, Vic.
    Posts
    838

    Default

    Can you post a picture of the Data Plate on the motor?

  5. #5
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,218

    Default

    I wonder if it is wired correctly. Sounds like one phase is not there.
    Gold, the colour of choice for the discerning person.

  6. #6
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    Quote Originally Posted by eskimo View Post
    are you sure you have 415v across all three phases at the motor terminals?




    are you saying the motor is a 2 speed motor? and you have tried to configure accordingly to work from the VFD on both speeds?
    I did check static and running but for some reason when running the voltage was jumping around too much for me to understand. Maybe my multimeter wasn't up to the task.
    Measuring from motor terminals while running multimeter also kept flipping over to DC.


    Yes 2 speed 700 and 2800 but haven't run it from the 700 side.

    According to those with the same motor it can only be run on one speed.
    woodworm.

  7. #7
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    Quote Originally Posted by Metalmachine View Post
    Maybe it dosen’t like too much variance from the 50Hz it was designed for?

    Unsure though as most people seem to rave on about how much range of speeds they can get from a vfd
    I could vary the speed quite a bit until it went too low.
    woodworm.

  8. #8
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    VFD maker data label.jpgEMB motor plate.jpg
    Quote Originally Posted by Techo1 View Post
    Can you post a picture of the Data Plate on the motor?
    woodworm.

  9. #9
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    Quote Originally Posted by .RC. View Post
    I wonder if it is wired correctly. Sounds like one phase is not there.
    Thinking now of bypassing lathe connections and wiring directly from VFD to the motor.
    woodworm.

  10. #10
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    Quote Originally Posted by Metalmachine View Post
    Maybe it dosen’t like too much variance from the 50Hz it was designed for?

    Unsure though as most people seem to rave on about how much range of speeds they can get from a vfd
    If I turn VFD up to 50hz, motor still won't start without a push, but once running I can vary speed with the VFD.
    woodworm.

  11. #11
    Join Date
    Jan 2004
    Location
    Mackay North Qld
    Posts
    6,446

    Default

    DISCLAIMER

    No liability is accepted by MetalWork Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradesperson for all electrical work.


    WARNING

    Information supplied within Electrical Posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk.


    Updated Nov 28 2022

  12. #12
    Join Date
    Aug 2021
    Location
    Sydney
    Age
    46
    Posts
    117

    Default

    The 3 phase motors I’ve seen run with a missing phase (when a phase was lost in the building) ran slowly and with obvious growling sounds.

  13. #13
    Join Date
    Sep 2008
    Location
    Riddells Creek, Vic.
    Posts
    838

    Default

    How have you got it wired into the lathe switches? The VFD should have Phase Loss Protection so it would not run at all unless 3 phases were available.

  14. #14
    Join Date
    Jul 2006
    Location
    Athelstone, SA 5076
    Posts
    4,258

    Default

    I am guessing that 1 phase is missing. Wire direct to motor as you suggest.

  15. #15
    Join Date
    May 2009
    Location
    sydney
    Posts
    183

    Default

    I've now noticed that the motor will keep running even when frequency is turned down to around 3.5hz
    woodworm.

Page 1 of 3 123 LastLast

Similar Threads

  1. Replies: 26
    Last Post: 20th Sep 2018, 07:35 PM
  2. Hamatu Lathe on Single Phase
    By GuzziJohn in forum METALWORK GENERAL
    Replies: 13
    Last Post: 18th Apr 2013, 09:24 AM
  3. Replies: 14
    Last Post: 4th May 2012, 08:48 AM
  4. Hercus 3 phase lathe, single phase supply
    By Pete F in forum THE HERCUS AREA
    Replies: 51
    Last Post: 16th Jan 2009, 10:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •