I am attempting to run a 1/2Hp 3ph geared motor from single Ph using a VFD. Using VFD because it is apparently cheaper and simpler regarding speed control, I need on/off forward/reverse and speed control,
problem is the motor has lost most of it's torque I am told that this is the result of using VFD.
What is recommended if I dispense with the VFD and just run 3Ph controller.
-
7th Aug 2022, 05:06 AM #2
Hi Bob,
This problem may be that the motor is intended to run on 380/400 volts three phase and your VFD only outputs 230/240 volts. The cure for this is to change the motor winding configuration from star to delta wound. Sometimes you can do the easily in the terminal box other wise its a strip down and hunting out the star point, splitting it to create three separate windings that you can reconnect in delta.
Check what it says on the rating plate ! Sometimes there are six terminals in the connection box along with three links. But this isn’t always a reliable method of determining whether the configuration can be changed there.
HTH.Best Regards:
Baron J.
-
7th Aug 2022, 10:08 AM #3Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,651
You can also get the step up VFDs that will convert 240v 1ph input to 380v 3ph output. A couple of common Chinese brands are Ecogoo or Nflixin
I've got mine from AliExpress, usually the Ecogoo store (all mine are Ecogoo ones).
There's a thread around somewhere about my experiences with them - search for "Ecogoo"
I've got 3 or 4 of them here now, and so far no failures or issues. The only negative with the small ones is that they really need to go in an enclosure as the physical terminal protection on them isn't great.
Steve
-
7th Aug 2022, 10:09 AM #4Most Valued Member
- Join Date
- Jul 2006
- Location
- Athelstone, SA 5076
- Posts
- 4,255
ditto what Barron and Steve say...and also is the VFD a vector drive type?.
-
7th Aug 2022, 10:26 AM #5Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,182
Maybe have a read of this document - I wrote it for the woodies forums but it could prove useful here too.
I might put it as a sticky in the electrical forum.
VFDs4Newbies2.pdf
-
7th Aug 2022, 11:20 AM #6Most Valued Member
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 9,088
I assume its covered in Bob's link but how sure are you that the VSD is setup correctly?
What VSD do you have?
"the motor has lost most of it's torque" At 50Hz, starting or something else?
The default settings on most of the VSD's I have result in "low torque". The default settings on the VSD are not what the manual says they are. I THINK it was base Freq set to 400Hz that was my issue.
-
8th Aug 2022, 01:02 AM #7China
- Join Date
- Dec 2005
- Location
- South Australia
- Posts
- 1,656
Thanks for the replies I will need to to some playing around will post to out come.
-
8th Aug 2022, 10:38 AM #8Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 831
Can you post a picture of the I/D plate on the motor?
-
8th Aug 2022, 11:05 AM #9Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,182
Apologies if I offended anyone with the title of the document on VFDs I attached.
Title has been amended.
-
8th Aug 2022, 12:03 PM #10Diamond Member
- Join Date
- Sep 2006
- Location
- Australind , WA
- Age
- 58
- Posts
- 1,277
Also, some VSD's can 'boost' the low speed torque of the motor, via a parameter or two.
That might help some.
-
8th Aug 2022, 02:07 PM #11Member
- Join Date
- Apr 2020
- Location
- Hackham West
- Age
- 55
- Posts
- 55
Hi...are you located in Adelaide?
-
8th Aug 2022, 04:58 PM #12China
- Join Date
- Dec 2005
- Location
- South Australia
- Posts
- 1,656
erick's 2
Morphett vale
-
8th Aug 2022, 05:00 PM #13China
- Join Date
- Dec 2005
- Location
- South Australia
- Posts
- 1,656
Techo 1
P1010457.jpg
-
8th Aug 2022, 05:10 PM #14
I will bet that the motor can be altered under the terminal box cover, look on the inside of the lid there is often a diagram showing how to change the motor configuration from star to delta.
Also have a read of this thread !
https://metalworkforums.com/f316/t20...sting-picturesBest Regards:
Baron J.
-
8th Aug 2022, 06:11 PM #15Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,182
I agree with BJ - the underlined 220-240D means it can be converted to delta
Chinamotor.jpg
However, unless powered by a vector drive VFD its output power is still only going to be proportional to frequency up to 50Hz.
ie
At 25Hz its going to be able to deliver 1/2 its rated power
At 12.5Hz . . . . . . . . . . . . . . . . . . . 1/4 . . . . . . . .
etc
Similar Threads
-
more questions
By fxst in forum THE FOUNDRYReplies: 5Last Post: 5th Apr 2013, 12:35 AM -
TIG questions
By Stumper in forum WELDINGReplies: 13Last Post: 4th Dec 2011, 09:57 PM -
questions #4
By burraboy in forum TRAILERS & OTHER FABRICATED STUFFReplies: 1Last Post: 18th Sep 2010, 05:40 PM -
questions #3
By burraboy in forum TRAILERS & OTHER FABRICATED STUFFReplies: 1Last Post: 7th Sep 2010, 10:41 PM -
tig questions
By welder in forum WELDINGReplies: 25Last Post: 4th Jul 2009, 10:55 PM