Needs Pictures: 0
Results 1 to 15 of 16
Thread: Single phase power monitor
-
27th Aug 2021, 10:57 AM #1Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,673
Single phase power monitor
Since I'm going to be stretching the friendship with my power supply when I get the new lathe going, I thought it would be a good idea to have some sort of power/current monitor in the shed. Needs to handle roughly 50A
I'm mostly interested in the total current draw at the shed switchboard, but it would be nice to have that info available remotely somehow rather than having to physically go to the switchboard to check.
If I was bored for a project I'd probably set something up with an Arduino and remote display or similar. Although it would be fun, I have plenty of projects already - definitely don't need another one!!
Any suggestions?
Steve
-
27th Aug 2021, 12:28 PM #2Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
I know what you mean and have thought about setting up something like you describe but every time it comes up I seem to move on mainly because when I'm doing something in the shed, like welding, I can't usually be simultaneously watching a power meter.
On a several occasions in the past I have got someone to watch the V/I meter on the switchboard while I perform a task, but more recently I just video the shed power meter using a mobile on a tripod I keep in the shed.
Some of my machines like the WW BS below have their own V/I meters.
The other machines that have this are the compressor and the Dust Extractor.
Electronics2.jpg
I also have two portable V/I meters.
This one has a 10A plug, a twin 15A GPO outlet and a 10A breaker.
PB1.jpg
This one has a 15A plug, a twin 15A GPO outlet and a 20A breaker.
It also has a power factor display.
PB2c.jpg
-
27th Aug 2021, 01:08 PM #3Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,673
Thanks Bob. Videoing the meter is a practical solution to capture whats happening.
Those meters that you've used, are they anything special or just whatever stuff you can find on ebay etc?
Steve
-
27th Aug 2021, 03:10 PM #4Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
They are all from ebay but there are some differences.
All 3 of the power meters in the photo are plugged into the same outlets.
A Digital multimeter in the same socket reported 249.6V
Meters.JPG
The other 3 B&W LCD power meters in the shed all read 249V (nothings drawing power )
The other green and red panel on the Band Saw read 258V
The B&W LCDs tend to be more accurate but over a few years they fade and I have replaced both of mine after about 5 years.
The red and green display ones are really cheap and I've only had them for a couple of years but noticed teh one on the bandsaw is starting to consistently read the Voltage too high.
-
4th Sep 2021, 01:00 PM #5Golden Member
- Join Date
- Dec 2007
- Location
- Adelaide
- Posts
- 575
We got one of these included in our solar power system, it might do what you want - a current transformer is placed on one of the AC power leads and through a battery powered dongle transmits to a 'base station' with a LCD display - the display then give a reading in Kw of the power going through the the AC cable. For a solar system 2 current transformers can be used so the base station can work out how much energy is being fed back into the grid - in your case only one current transformer needs to be used as you are only monitoring the power being used in the shed or lathe - the current transformers simply clip on to one of the power cables either active or neutral much like an AC clamp meter, the base station is wifi enabled so you can download an app and monitor remotely via the internet on a mob phone, our transmitter dongle sits in the meter box and I have had the base station up to 30 meters away, at present it is only around 10 meters away, there are other brands available.
https://www.ebay.com.au/itm/33327184...frcectupt=true
-
4th Sep 2021, 02:38 PM #6Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Minor point, but because breakers and wiring are rated in terms of current, that is what I prefer to see on display rather than the power.
-
5th Sep 2021, 01:33 AM #7Golden Member
- Join Date
- Dec 2007
- Location
- Adelaide
- Posts
- 575
If it's just AC amps you need to check then a digital clamp meter will do it - the fancy ones have peak hold and even connect to a mobile phone for remote monitoring.
-
5th Sep 2021, 09:36 AM #8Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
I have two current clamps but to use them they must be clamped around the active or neutral which can be a PITA. To make things easier I made up a short split cord extension cord to plug in line between an outlet and the machine, but some machine's plug/socket are not well placed to be able to see the meter easily while operating which is when I want to see the current. For about $10ea those V/I panel meters can be permanently mounted on a machine in an easily/safe readable location.
As far a using a mobile in a workshop goes, while I use a number of mobile Apps (including SPL, light intensity, vibration, air flow, calculator) in the workshop, I generally don't like using a mobile phone in there especially while actually operating a machine so I only do this on occasional basis. The main issue I have are where to put it safely while using the machine and then remembering where I put it. To get around this I sometimes use my home mADE mobile cradle mounted on a photographic tripod but doing this for a quick current measurement is a PITA.
MkIIV.jpg
But given how cramped and cluttered my shed is, I don't want to be doing this on a regular basis. I really dislike the general fiddling involved with using a mobile, especially in a workshop, stopping to find the effing phone, has it got enough charge, fingerprint password not working due to dirty hands, getting the thing dirty etc.
-
5th Sep 2021, 07:48 PM #9Diamond Member
- Join Date
- Jun 2010
- Location
- Canberra
- Posts
- 1,322
I recently got one of these:
https://stuff.iotawatt.com/product/a...v=6cc98ba2045f
And a bunch of their 50A CTs and went to town on our switchboard, 3 CTs for the house, 3 for the workshop, one for the offpeak hot water and one for the solar.
The goal is to try and optimise the use of solar generation using automation to switch on loads when there's excess power being exported to the grid.
The unit has inbuilt graphing, and you see individual loads show up on the different phases, which, among other things, is useful for seeing if the phases are reasonably balanced - for example, I've made sure my plasma cutter is on a different phase to the air compressor.
-
5th Sep 2021, 10:47 PM #10Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,673
Thanks Rusty - that’s interesting. Looks like a very flexible piece of kit, and the price isn’t over the top. I’m a sucker for relatively open systems too
I’ve got a couple of cheap VI meters and transformers ordered and in the post somewhere which will get me started - but the IoTaWatt is the sort of thing I was originally thinking of.
Steve
-
9th Sep 2021, 02:34 AM #11
Hi Steve, Guys,
A real easy way is to simply measure the voltage drop across the feed cable !
Since a volt meter (Multimeter) draws essentially no current a suitably insulated thin wire could be used to connect the meter to either end and would be quite adequate if not particularly practical. Of course you would have to know the length and resistance of the feed cable, but that would give you an instant value as the load changed.
A current transformer would do the same thing but also requires a load resistance to measure across and be safe. You would only put one on each feed wire in a three phase system or just the live wire in a single phase system. The advantage is that it can be put at either end or anywhere along the feed wire and the reading will be exactly the same.
Does the VFD have the ability to display load current ?Best Regards:
Baron J.
-
9th Sep 2021, 10:10 AM #12Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Not sure I would call it easy, especially if it was required to be left insitu
I have experimented this method and the main problem especially with short power leads in decent condition is the lead resistance is generally too low for basic multimeters to measure.
A 1m length of 1.75 mm diameter Cu wire has a resistance of about 0.006Ω.
For a 10A current and a 3m length of cable that's a V drop across the cable of ~0.2V.
Most basic basic meters would measure 250V to no better than 0.1V so at a minimum there's a +/- of 50%
The other issue when accurately measuring the resistance of low resistance cables is contact resistance.
Unless screwed down terminals are use just poking a couple of meter probes at the bare cable is unlikely to produce accurate resistance measurements.
To get semi consistent results I ended up using longer (eg >10M) cables.
To do this accurately the cable has to be uncoiled or the inductance effect will dominate the voltage drop.
This meant I ended up with lengths of cable all over the floor
Using thinner cables is a possibility but that has its own problems.
Going back to the contact resistance problem to further complicate things, when I tried it, I inserted "thru" plug at both ends of the cable to act as meter test points but the contact resistance of the plugs was not consistent until i polished them with some steel wool, Plugs are easy to polish but sockets are not.
It was after mucking about with these methods I resorted to cheap panel meters.
-
9th Sep 2021, 10:52 AM #13Golden Member
- Join Date
- Dec 2007
- Location
- Adelaide
- Posts
- 575
BobL you sound like you are on the ball with all this, not sure if you are aware but while Chinese AC digital panel meters are cheap and easy to use they can be non linear, most seem to be based on a 200mV ac meter that has had shunts and or multipliers added so larger voltages and currents can be measured. I was going to use one in a project and decided to check out the linearity when compared to my Fluke 87, it was accurate enough from 200mV down to 20 mV when the meter started to read under, getting worse as the voltage dropped - at around 10mV the error was almost 30%, there are probably instances where this doesn't matter as the voltage/current being monitored never drops that low, but in my case it was a no go.
I suspect the error comes from the panel meters using a precision rectifier to do the AC to DC conversion rather than a more expensive AC to DC true RMS dedicated chip, there probably are AC digital panel meters out there that are linear but I doubt they are the ones that abound on ebay for $15 or $20.
-
9th Sep 2021, 01:36 PM #14Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,673
Thanks John.
There's actually a shunt in the DSG lathe that's intended to run a ammeter, and the VFD can display current on its panel (manual says its output current but I'm not convinced). Likely its available to read via RS485 too.
So its not that I don't have methods of getting the data, but looking for a more convenient way to monitor and display.
Steve
-
9th Sep 2021, 01:39 PM #15Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Yes that is more or less what I see as well but it does vary from meter to meter.
Here are a few readings I quickly cobbled together.
I usually question any readings less than 1A on these panel meters - if I need to measure below this I get out the Fluke.
Meter A (blue dots - a DIN rail meter) is not too bad above about 0.5A but everything else is at best indicative at low values.
I use the panel meters mainly to observe currents when machines are under load so this is usually above 5A
Screen Shot 2021-09-09 at 10.31.52 am.png
Similar Threads
-
Anyone running 3 phase coolant pump on single phase?
By Com_VC in forum ELECTRICALSReplies: 21Last Post: 26th Oct 2018, 08:47 PM -
415v three phase from 240v single phase a home made digital phase converter?
By lamestllama in forum ELECTRICALSReplies: 26Last Post: 20th Sep 2018, 07:35 PM -
Homemade rotary converter 230v single phase to 415v three phase (Video)
By Tilly819 in forum ELECTRICALSReplies: 0Last Post: 27th Jul 2018, 09:12 PM -
Huanyang VFD - How to get single phase outputs from VFD 3 Phase output points (U,V,W)
By AP-R*D in forum METALWORK GENERALReplies: 14Last Post: 4th May 2012, 08:48 AM -
Hercus 3 phase lathe, single phase supply
By Pete F in forum THE HERCUS AREAReplies: 51Last Post: 16th Jan 2009, 10:15 AM