Ecogoo VFD Error Code
One of my Ecogoo 240v single phase input to 380V 3phase output VFD's has tripped out with an OCH error code, the problem is that this particular code is not listed in the Instruction Manual. Has anyone experience this?
-
16th May 2021, 11:35 AM #2Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,182
What HP ratings are the VFD and motor?
When does the error occur, on startup, unloaded motor, loaded motor???
Sounds like it could be an Over Current error.
My understanding is those VFDs don't allow the user to set a current limit but if it does, try reducing the max current.
-
16th May 2021, 02:51 PM #3I break stuff...
- Join Date
- Aug 2010
- Location
- Toorloo Arm, VIC
- Age
- 39
- Posts
- 1,270
Overcurrent. Same code mine threw when this happened (quote pinched from my Graziano thread.) And yes, annoying that the manual doesn't match up to it, but not unusual.
In this case the cause was pretty clear, but I think it's worth commenting that the HuanYang on the mill for some weird reason trips out with some sort of error if I crank the varispeed handle too fast when slowing it down. Doesn't do it under any sort of cutting load, just if you spin the speed changer down too fast, and has done it for years.
So the cause may or may not be something sinister, depending on the circumstances... Potentially trying to brake the spindle/motor too fast could do it (short decel time), I always just set mine to 'coast'...
I assume with this you're referring to a current limit which keeps the motor running, whilst not allowing it to draw over X amount of current?
The EcoGoo has a section for motor parameters including current, but as far as I can tell exceeding that just trips a fault, so reducing the current would make things worse if there was a persistent problem...
-
19th May 2021, 08:09 PM #4Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 831
The motor is 2 speed, 1.2kw on high speed. The VFD is 2.2kw (see photo of motor data plate). I think this error is fatal as I cannot get rid of it.
Attachment 392156
-
19th May 2021, 08:18 PM #5Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,182
Did you leave the 2 speed switch in place and did you try switching speeds with the motor running
-
21st May 2021, 09:29 AM #6Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 831
-
22nd Aug 2023, 10:56 AM #7Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 831
Just a follow up on this thread for anyone with this same problem: after replacing one of the six IGBT's with a new item from Aliexpress the drive is now running like new.
Ecogoo vfd.jpg
IGBT.jpg
-
22nd Aug 2023, 06:24 PM #8Golden Member
- Join Date
- May 2020
- Location
- Willowbank QLD
- Posts
- 516
How did you determine which IGBT was the problem child? Good fault finding.
Steve
-
23rd Aug 2023, 01:43 PM #9Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 831
Similar Threads
-
Ecogoo 1ph 220v to 3ph 400v inverter - experiences
By OxxAndBert in forum ELECTRICALSReplies: 95Last Post: 24th Oct 2021, 06:49 PM -
Ecogoo single to three phase inverter set up
By Tinkerer77 in forum ELECTRICALSReplies: 6Last Post: 9th May 2021, 05:20 PM -
Enco 15% off code
By Greg Q in forum METALWORK GENERALReplies: 0Last Post: 17th May 2013, 01:13 AM -
Error in the FAQ - BBCode/vB code
By Skew ChiDAMN!! in forum FORUMS INFO, HELP, DISCUSSION & FEEDBACKReplies: 7Last Post: 28th Sep 2009, 12:26 AM