    Default Unusable compressor

    I have a Peerless compressor 545l/min. delivery which I run through a phase change convertor and have had no problems with it until my neighbour complained to Essential energy that the street voltage was causing problems with his solar system - they subsequently reduced the voltage in the
    street which caused me not being able to start my compressor - how can I determine where the fault lies here ? is it my phase change convertor, the supply voltage to it or the compressor itself and can anyone one of you advise how I can overcome my problem as I am not very electrically wise
    I could change the motor to 240V but what HP would I need (the existing is 5.5 HP) and can I be sure this will fix the problem
    Essential energy in a previous look at my problem advised that the street voltage is within its tolerances so that's it
    My neighbour suggested A VFD but I don't know what that would do or if it would overcome my problem
    Over to you gentlemen

  2. #2
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    Sounds like it may have been marginal anyway, if reducing the supply voltage made that much difference.
    Are you able to measure the supply voltage now, and do you know what it was?
    How is the phase converter connected? If there is an extension lead, make it as short and heavy as you can.
    Is the current motor 240 or 415? If it's 240 a vfd may replace the phase converter successfully, if it is 415 there are also vfd available but at a higher price.
    As to what the fault is, a bit hard to tell but developing a fault at the same time the power company did work does seem not probable.

    If this is all foreign, perhaps you should see if you can find a friendly industrial electrician.
    Where are you located? Maybe local forumite may be able to help

  3. #3
    Join Date
    Sep 2012
    Location
    York, North Yorkshire UK
    Posts
    6,439

    Default

    Hi Alf, Guys,

    I think that I would plump for a 240 volt single phase to 440 volt three phase VFD ! Certainly it would be more cost effective !
    Best Regards:
    Baron J.

  4. #4
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,216

    Default

    If it is a Phase Change converter, have you contacted them?
    Gold, the colour of choice for the discerning person.

  5. #5
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    A 5.5HP motor may represent a bit of a problem because 240V SP to 415V 3P VFD don't usually come in that size typically the biggest they get is 5kW.

    Ordinarily a 5HP VFD would cope with that but because motor max HP is critical for compressors running a 5.5HP motors on a 5HP VFD might overload the VFD.
    Chances are the motor is generating even more that 5.5HP for the last 20 or so PSI of its charging cycle

    A few years ago I attempted to run a 4HP compressor from a 4kW (240V-415V) VFD and it would not get past 100PSI which is where the motor drew ~15A (240V) and with the max setting current of VFD of 12.5A this tripped the VFD. I got around this by using a 5HP VFD but when that motor died I replaced it with a 240V 4HP motor.

  6. #6
    Join Date
    Nov 2017
    Location
    Geelong, Australia
    Age
    57
    Posts
    2,651

    Default

    When you say that the compressor won’t start, what actually happens when you try?
    Does it try to start then trip a breaker/overload somewhere?

    Do you run any other gear off the converter? If so is that behaving normally?

    I find with troubleshooting it’s very tempting to jump to an initial conclusion about the source of the fault, but often it’s something completely unrelated.

    I’d start with the simple things - remove the belts and make sure the motor runs happily unloaded.

    If it does, then completely depressurise the tank and try again.

    It could be something as simple as the unloading function on the compressor isn’t working and it’s trying to start with the full pressure load on the pump.

    Steve

  7. #7
    Join Date
    Mar 2011
    Location
    Taree NSW
    Posts
    119

    Default unusable compressor

    Quote Originally Posted by OxxAndBert View Post
    When you say that the compressor won’t start, what actually happens when you try?
    Does it try to start then trip a breaker/overload somewhere?

    Do you run any other gear off the converter? If so is that behaving normally?

    I find with troubleshooting it’s very tempting to jump to an initial conclusion about the source of the fault, but often it’s something completely unrelated.

    I’d start with the simple things - remove the belts and make sure the motor runs happily unloaded.

    If it does, then completely depressurise the tank and try again.

    It could be something as simple as the unloading function on the compressor isn’t working and it’s trying to start with the full pressure load on the pump.

    Steve
    Thanks to all who answered - when connected to any other 3 ph. machines I have no problem
    To be able to use the compressor I have fitted a ball valve to each head , started the comp. with valves open then closed them when comp. is up to speed - there was never any trouble until Essential energy played with the supply - both my lathe and mill give me no trouble starting- the ball vlvs are a PITA and aren't the answer

  8. #8
    Join Date
    Mar 2011
    Location
    Taree NSW
    Posts
    119

    Default unusable copressor

    Quote Originally Posted by OxxAndBert View Post
    When you say that the compressor won’t start, what actually happens when you try?
    Does it try to start then trip a breaker/overload somewhere?

    Do you run any other gear off the converter? If so is that behaving normally?

    I find with troubleshooting it’s very tempting to jump to an initial conclusion about the source of the fault, but often it’s something completely unrelated.

    I’d start with the simple things - remove the belts and make sure the motor runs happily unloaded.

    If it does, then completely depressurise the tank and try again.

    It could be something as simple as the unloading function on the compressor isn’t working and it’s trying to start with the full pressure load on the pump.

    Steve
    Starts and dies before reaching full speed
    Shuts down the phase convertor which then restarts itself
    runs my mill and lathe no problem
    thanks for help

  9. #9
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    It does sound like low voltage, which causes increased start up current which trips the phase converter.
    The phase converter is a commercial unit? Does it have any adjustment to the output voltage, eg different transformer taps.
    It also sounds like the compressor is starting under load. If the tank is empty does it start ok?

    The other machines you mentioned are not likely to be pulling a full load on starting, or probably ever.

    Do you know what your supply voltage is, and what it was?

  10. #10
    Join Date
    Aug 2019
    Location
    Revesby - Sydney Australia
    Age
    56
    Posts
    1,183

    Default

    Is there a long cable run to your shed?

    That might be pushing the (now in spec?) voltage below the threshold for your converter?


    (a true RMS voltmeter is your friend)

  11. #11
    Join Date
    Sep 2010
    Location
    Lebrina
    Posts
    1,910

    Default

    I am far from an expert on this subject, but as a matter of interest, do you know what the supply voltage was before the change and what it is now?
    My single phase compressor has an unloader built into the pressure switch so the motor gets up to speed before the load comes on, while my 3 phase unit does not, (it does however have a 10Hp 6 pole motor running a 40 CFM pump, so no shortage of Hp).
    It sounds to me that you may have been running on the borderline and the reduced voltage has tipped you over the edge. Assuming your electrics all check out, then an automatic unloader valve may be your friend.

  12. #12
    Join Date
    Mar 2011
    Location
    Southern Flinders Ranges
    Posts
    1,536

    Default

    Correlation does not equal causation
    If you have other equipment that runs on the phase converter and the compressor used to run on the phase converter but now doesn’t, the compressor has an issue of some description.
    Line voltage is regulated within prescribed limits, any equipment you connect to line will run within those limits.

  13. #13
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,216

    Default

    If it is a phase changer converter, maybe the capacitors are getting tired. I have replaced a few of mine as they started leaking. They are reasonably cheap.
    Gold, the colour of choice for the discerning person.

  14. #14
    Join Date
    Sep 2008
    Location
    Riddells Creek, Vic.
    Posts
    831

    Default

    What model Phase Changer is this Alf?

  15. #15
    Join Date
    Mar 2011
    Location
    Taree NSW
    Posts
    119

    Default unusable compressor

    Quote Originally Posted by Techo1 View Post
    What model Phase Changer is this Alf?
    Phase changer 6
    Voltage is within Essential energies tolerances but they say maybe the cable dia. to the shed is a problem - long run and 10 mm. dia. cable ?
    Will be contacting phase changer people this week for comment, trouble is each want to blame the other so I am going around in circles here

Page 1 of 2 12 LastLast

Similar Threads

  1. Compressor ID help
    By bts in forum METALWORK GENERAL
    Replies: 4
    Last Post: 9th Sep 2020, 07:21 PM
  2. What oil for air compressor?
    By Com_VC in forum METALWORK GENERAL
    Replies: 25
    Last Post: 14th Aug 2018, 09:20 PM
  3. Air compressor
    By Turbine Builder in forum METALWORK - Machinery, Equipment, MARKET
    Replies: 2
    Last Post: 29th Jul 2018, 06:03 AM
  4. May need another compressor... How big.. Used or New??
    By ventureoverland in forum METALWORK GENERAL
    Replies: 25
    Last Post: 25th Jan 2015, 09:21 PM
  5. air compressor
    By mirage1 in forum METALWORK GENERAL
    Replies: 3
    Last Post: 13th Jul 2006, 11:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •