    Default Is a con VFD output voltage

    I just bought the cheapest VSD on eBay a mistake I know. turns out it's an Isacon 1.5kw I tried to set it up tonight and .. . Nothing the motor makes the VFD wine but doesn't rotate. I Get the meter out and it is indeed 50hz but the output voltage is only 48volts. My question is the drive cactus which I suspect and I hopefully can get a refund or am I missing something .
    BETTER TO HAVE TOOLS YOU DON'T NEED THAN TO NEED TOOLS YOU DON'T HAVE

    Andre

  2. #2
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Do you have manual and have you read it?

    VFDS are rarely plug and play so unless you have a lot of experience expect to do a couple of hours of homework with the manual BEFORE you connect it to a motor.

    Have you done a factory reset - that's the first thing I would do on a used unit - I even do that on new ones after a new VFD tried to drive a motor up to 400Hz!

  3. #3
    Join Date
    Mar 2008
    Location
    nowra
    Posts
    1,598

    Default

    Bob the manual on these units Is rubbish. They have very limited settings I haven't even found a mention of a factory reset in the manual.
    BETTER TO HAVE TOOLS YOU DON'T NEED THAN TO NEED TOOLS YOU DON'T HAVE

    Andre

  4. #4
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by welder View Post
    Bob the manual on these units Is rubbish. They have very limited settings I haven't even found a mention of a factory reset in the manual.
    Oh dear, my number one tip when buying a new VFD is makes sure it has a manual that you can understand.
    Even more important for a used one.
    Sorry.

  5. #5
    Join Date
    Mar 2008
    Location
    nowra
    Posts
    1,598

    Default

    Yea these drives aren't anything like a Powertran or a HY. I just wanted a cheap drive for a 3 phase machine I
    Wish to sell. I just find it strange it's only putting out 48volts.
    BETTER TO HAVE TOOLS YOU DON'T NEED THAN TO NEED TOOLS YOU DON'T HAVE

    Andre

  6. #6
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    3,228

    Default

    Quote Originally Posted by welder View Post
    ...the motor makes the VFD wine but doesn't rotate.
    Is it performing an auto-setup? They make that whine when they are measuring the motor’s parameters.
    Chris

  7. #7
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by jack620 View Post
    Is it performing an auto-setup? They make that whine when they are measuring the motor’s parameters.
    Usually that requires the motor to be running.

  8. #8
    Join Date
    Dec 2007
    Location
    Adelaide
    Posts
    574

    Default

    How long did you try it for - perhaps it has been set for a long ramp up time, a vfd is not like mains power where the motor comes on instantly they do take a few seconds to come up to full speed.

  9. #9
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    If you post the manual or a link the collective may spot something...

    Russ

  10. #10
    Join Date
    Aug 2008
    Location
    Charlestown NSW
    Age
    65
    Posts
    1,669

    Default

    this is the user manual for an ISACON HY serieshy book.pdf

    I bought one of these the weekend before last, mistakenly thinking it was a Huanyang.

    I think PN32 (page 16) allows you to reset to the factory setting.
    I also found some more info here.

    peter

  11. #11
    Join Date
    Dec 2007
    Location
    Adelaide
    Posts
    574

    Default

    On page 9 there is a setting Acceleration Time PN08 factory default is 10S (10 seconds ?) in the 50Hz column perhaps check this out you may need to set this for something a bit more practical like 3 or 4 seconds I've heard some VFD's don't like a setting much lower than this and they will go into overload due to the amount of current draw over short time so if this is the problem you may need to experiment a bit with settings.

    I had a similar issue with my lathe VFD and the jog button, the jog frequency was set to I think to 7 or 8 Hz and the jog acceleration time was set for around 5 or 6 seconds - on pressing the button I had no motor action so I went looking for wiring errors, after much checking I spent some time with the manual and eventually realised I did not wait long enough for the motor to start. Resetting the acceleration time to a shorter time fixed the problem.

  12. #12
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    My guess is Pn12=400. To start with you want Pn12=50
    All my HY's came set to 400 regardless of what the manual states.
    While you are in there check Pn10=50.

  13. #13
    Join Date
    Aug 2011
    Location
    Melbourne
    Posts
    4,779

    Default

    How did you end up going with tht VFD Andre?

    I need a couple of VFD's and was going to buy those cheapies but I need the basic functions such as ramp up, ramp down V/F curve customisation and jog.

    Simon
    Girl, I don't wanna know about your mild-mannered alter ego or anything like that." I mean, you tell me you're, uh, super-mega-ultra-lightning babe? That's all right with me. I'm good. I'm good.

  14. #14
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by simonl View Post
    How did you end up going with tht VFD Andre?

    I need a couple of VFD's and was going to buy those cheapies but I need the basic functions such as ramp up, ramp down V/F curve customisation and jog.

    Simon
    Simon, I'd make sure you can read and understand the manual first.

Similar Threads

  1. DC stepper motors voltage??
    By KBs PensNmore in forum ELECTRICALS
    Replies: 1
    Last Post: 18th Aug 2016, 07:24 PM
  2. motor output shaft sizing
    By Harry72 in forum METALWORK GENERAL
    Replies: 11
    Last Post: 26th Apr 2016, 09:06 AM
  3. Replies: 14
    Last Post: 4th May 2012, 08:48 AM
  4. voltage settings aust / usa
    By old mate in forum WELDING
    Replies: 3
    Last Post: 18th Jul 2010, 06:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •