9th May 2019, 06:23 PM #16Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
That's it - its all in the manual,
Step one; setup switches and wiring as per page 19 in the manual.
eg DI1 terminal is normally set as default to Run.
One terminal of teh switch gies to DI1 the other goes to COM.
Switch closed VFD starts, switch one VFD stops.
Screen Shot 2019-05-09 at 3.15.01 pm.png
Step 2: Then you have to set F0.11 to 1 so that the external switches will work
(default for F0.11 is 0 - front panel)
Step 3 Set the Correct codes for the DIs
P33 shows what to set the DIs to using F1.00 to F1.08
See how F1.00 is already set at 1 and chart below shows that 1 = Run/FWD,
F1.01 is set for 2 ie REV.
I do this on the same switch with 3 positions, eg up = FWD, middle = stop, down - REV
No D! need be used for a stop.
To set a FWD jog set up a switch connected to any unused DI terminal (other end to com) and set the corresponding F1.0x to 4, or 5 for rev Jog.
Screen Shot 2019-05-09 at 3.10.03 pm.png
-
9th May 2019, 07:54 PM #17Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
Awesome - I certainly didn't expect that level of detail!!
Thanks Bob
My next question was going to be how to control the speed if the front panel was no longer active, but looks like I can set F0.11 to 4 and have the front panel and the terminal block enabled at the same time.
So should be able to still use the pot on the front panel to control the frequency.
Steve
-
9th May 2019, 09:07 PM #18Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
-
9th May 2019, 09:44 PM #19Diamond Member
- Join Date
- Oct 2008
- Location
- N.W.Tasmania
- Posts
- 1,407
Certainly not trying to undermine or argue with you Malb, I never have been an engineer, not even his bootlace, but as the OP is going to use a 4Kw inverter on a 3Kw motor, and intends to use very soft starts and stops, I would imagine that the rectifier diodes will most likely remain fairly unstressed. Bearing in mind, a milling machine in hobbyists hands would rarely be fully loaded, (unlike some production machines, which are often loaded to capacity), and the possibility that the rectifiers could be specced for 480V or single phase operation, the chances are that he should be pretty safe. Of course a crash, or workpiece coming loose and causing a jam could change all that in a few milliseconds. Hopefully the rectifier bridge is fairly easily replaced if it becomes necessary, and not firmly soldered to the main board, should my theory be proved quite wrong.
-
9th May 2019, 10:32 PM #20Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Powtran still don't make such a beast but Sako does, their SP220 to 3P380 models are called SKI670.
Here is a 7.5kW unit - note the AU$ 415 price and $135 shipping !
https://www.aliexpress.com/item/Sako...3-13bf7f1e2932
4kW for AU$230 and AU$79 shipping
https://www.aliexpress.com/item/Sako...3-13bf7f1e2932
Full range here
https://www.aliexpress.com/wholesale...KI670+SAKO+VFD
-
22nd May 2019, 03:32 PM #21Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
Trouble with the "parameter names" in the manual is that they are a bit open to interpretation.
eg F0.02 Frequency command resolution ==> options are 1:0.1Hz, 2:0.01Hz ==> default is 2.
So I think hmmm - that sounds like it would just change the coarseness of the frequency adjustment via the input panel pot.
WRONG!!
It changes the resolution of the frequency that is already set, so if your frequency was set to the default 50.00Hz and you change the resolution setting to "1" you end up with 500.00Hz
Things got a bit exciting there for a few seconds....so a smidgen gun shy now...
Trying to set a maximum frequency of 75Hz (already set in F0.19 MAXIMUM OUTPUT FREQ)
And be able to control it via the pot on the control panel (think this requires also setting F0.21 UPPER LIMIT FREQ ==> 75, and F0.20 UPPER LIMIT FREQ SOURCE ==> 3 (Panel encoder)
Does that sound right?
Steve
-
23rd May 2019, 03:04 PM #22Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
For reference, this is what I ended up with to set max freq to 75Hz and allow it to be controlled by the control panel pot while running:
F0.03 FREQ SOURCE MASTER ==> 4 (panel potentiometer)
F0.19 MAXIMUM OUTPUT FREQ ==>75
F0.20 UPPER LIMIT FREQ SOURCE ==> 3 (Panel encoder) **May not be 100% necessary**
F0.21 UPPER LIMIT FREQ ==> 75
Steve
-
28th Nov 2019, 04:26 PM #23Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
I just stumbled across this quickstart guide to programming one of these Powtran PI500 VFD's.
It shows a bunch of different scenarios for how you might set up external control etc.
http://www.anlauf.klibo.de/fileadmin...ion%202017.pdf
Steve
-
6th Apr 2020, 11:57 AM #24Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
Digging up this older thread as I'm currently in the process of finalising this install.
Regarding external speed control, the manual for this Powtran VFD says to use a 1Kohm 2W pot.
I've currently got it running fine on a 25K pot - not sure what its power rating is but the pot is around 20mm diameter. Its just one I had sitting in my stash so won't be anything special.
Should I bother sourcing a 1K 2W item, or just run with what's working now.
I'd prefer to do it properly from the beginning rather than have having issues in the future.
Steve
-
17th Apr 2020, 12:08 AM #25Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
Just in case it helps anyone else, after doing an auto-tune for the motor in vector mode I found I was getting a 06 error (deceleration overvoltage).
Look like the auto-tune changes the deceleration time (F0.14) and my case it was now only 2 seconds.
Not sure what it was originally as I didn't change it and the manual says the default "depends on models", but I increased the value to 6s and the error no longer occurs.
Possibly its a byproduct of doing an auto-tune with the motor still attached to the mill, and with the spindle in gear. I know you shouldn't auto-tune with a load connected, but thought the empty spindle wouldn't be an issue. That might have been a bad call.
Steve
-
17th Apr 2020, 02:27 PM #26Most Valued Member
- Join Date
- Mar 2011
- Location
- Southern Flinders Ranges
- Posts
- 1,552
That error is a warning that you have too much voltage on the bus caused by too fast a deceleration rate. A braking resistor would fix it, as does slowing the deceleration ramp as you have done.
-
17th Apr 2020, 02:41 PM #27Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,669
Yes, thankfully the Powtran manual is pretty good with the error descriptions.
Supposedly doing an auto-tune is recommended, but there's nowhere that I can find that has details of what parameters it changes.
I expected it to be internal profile black magic stuff to work out the optimum way to drive the motor, but didn't expect it to be messing with accel/decel times. I thought those would be related to the application rather than the motor itself.
I guess the takeaway is don't be surprised if you get some errors and have to re-tune parameters after the auto-tune has messed with them!!
Steve
Similar Threads
-
MMD-45 Mill Tight Spindle
By Oldneweng in forum METALWORK GENERALReplies: 39Last Post: 24th Oct 2014, 05:54 PM -
High Speed Spindle for the Mill
By RayG in forum METALWORK GENERALReplies: 10Last Post: 11th Sep 2012, 02:44 AM -
Where to buy DM45/46 Mill with R8 spindle?
By variant22 in forum METALWORK GENERALReplies: 16Last Post: 27th Aug 2012, 11:01 PM -
Need Some Advice: Level up Spindle on HM-46 Mill
By Jarh73 in forum METALWORK GENERALReplies: 9Last Post: 19th Apr 2011, 02:45 PM -
Mill Spindle Bearing Grease
By markjaffa in forum METALWORK GENERALReplies: 12Last Post: 7th Jun 2010, 11:51 AM