    Default 415v three phase from 240v single phase a home made digital phase converter?

    I don't have three phase at my place and getting it would be expensive. With that in mind I set up an experiment that has been a few months in the making (I had to wait for Kryn to bring me a crucial part from Melbourne). The picture shows a 240V VFD (only 1.5kw here) connected to an 8Kva three phase autotransformer.
    IMG_20180831_151936.jpg
    The autotransformer was originally designed to take three phase 415v and output 230v three phase but I run it in reverse. Setting the VFD to ramp up to 50hz at 240v over a few seconds avoids an over current situation when switching the thing on . I connected my unmodified Colchester Bantam to the output of the transformer and was happy to see it run with direct online starting without any issues. As expected the inductance of the transformer avoids any over current situation at the VFD when the motor starts.

    As mentioned this was using only a 1.5kw VFD I intend getting something around the 4kw mark so as to more fully utilise the capacity of the transformer any suggestions here would be welcome.

    The voltage out of the transformer even in reverse is around 400v so close enough.

    Anybody see any problems using this as a phase converter?

  2. #2
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    915

    Default

    Cool. Interesting concept.
    So the VFD is already running (at 50hz) when you switch on the motor?
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  3. #3
    Join Date
    Aug 2013
    Location
    Melbourne
    Posts
    229

    Default

    For interest, have a look at Dynoguy on YouTube, l think he does a similar setup
    https://youtu.be/UA9-jXlw4r4

  4. #4
    Join Date
    Jul 2011
    Location
    Adelaide
    Posts
    837

    Default

    Yes it is running at 50hz before the motor gets turned on. It has to run at 50hz so that the output is 400v so that the contactors in the lathe will work as normal. The plan is not to have to modify machines before they can be used.

  5. #5
    Join Date
    Nov 2017
    Location
    Geelong, Australia
    Age
    57
    Posts
    2,651

    Default

    Looks like a nice idea to me. I've seen those 3 phase step-down transformers around either cheap or free and it looks like it will give you the advantages of a phase converter that you just just plug 3 phase 400v gear into without the issues of a rotary converter.

    Steve

  6. #6
    Join Date
    Jul 2011
    Location
    Adelaide
    Posts
    837

    Default

    Quote Originally Posted by Petip View Post
    For interest, have a look at Dynoguy on YouTube, l think he does a similar setup
    https://youtu.be/UA9-jXlw4r4
    He puts the transformer before the VFD. I put the transformer after the VFD for two reasons. I have a machine that needs a neutral which I can get from a three phase autotransformer connected in Y. The other reason is the dampening effect the transformer has on the noise from contactors.

  7. #7
    Join Date
    Sep 2012
    Location
    York, North Yorkshire UK
    Posts
    6,434

    Default

    Hi,

    If you vary the VFD frequency a little, you should be able to find the sweet spot for the transformer output.
    Best Regards:
    Baron J.

  8. #8
    Join Date
    Jul 2011
    Location
    Adelaide
    Posts
    837

    Default

    Quote Originally Posted by BaronJ View Post
    Hi,

    If you vary the VFD frequency a little, you should be able to find the sweet spot for the transformer output.
    Hi BaronJ,

    Sweet spot in what way?

  9. #9
    Join Date
    Sep 2012
    Location
    York, North Yorkshire UK
    Posts
    6,434

    Default

    Hi,

    If you measure the output voltage, you will find that there is a point where the voltage increases or falls with changing frequency. The sweet spot for that transformer will be where the voltage peaks. The better the quality of the transformer the shallower the voltage peak will be.

    So for instance if at 50hz you get 400 volts and at 60hz you get 405 volts, but at 70hz you get 395 volts, then 60hz is closest to the sweet spot. The reverse is the same. If the voltage rises at 40hz then the transformer favours the lower frequency.

    You may not see much of a change in which case you have a good transformer. Do it under load as well the change will be more marked. The difficulty making measurements under load using the motor is that the load will change slightly with motor speed.

    Let me know what you find.
    Best Regards:
    Baron J.

  10. #10
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Cool idea but I'd like to see what happens when the motor is switched on or off under load. OK this is is unlikely to happen except in an emergency but I don't think the VFD will like it much as the transformer may not be able to protect the VFD.

    The way to get around this would be to wire emergency switches to turn off the VFD and I do mean cut the mains to the VFD.

    Are you using any of the other features of the VFD?, eg speed and braking controls?

    I can see it being useful on 415V delta machines with built in motors.

    As mentioned this was using only a 1.5kw VFD I intend getting something around the 4kw mark so as to more fully utilise the capacity of the transformer any suggestions here would be welcome.
    Does this mean you intend running more than one machine from the VFD? I would be be interested to see how that goes.

    I like Baron J's idea of tweaking the frequency to improve the transformer output but bear in mind that using V'F mode VFDs motors develop less power below 50Hz so there m ay not be any gain. I'm not sure if vector drive characteristics will transfer though a transformer. BTW Vector drives have to be tuned to a specific motor so this feature can't be used in a multi motor situation anyway.

  11. #11
    Join Date
    Jun 2008
    Location
    The Whitsundays
    Posts
    229

    Default

    I have thought of this setup in the past. I assume the VFD supplies 3 phases at 240 volts with no neutral? If I have that wrong please correct me.

    Your created "neutral" has no relationship to earth. A consequence is that any out of balance loading may cause a voltage rise on your "neutral". The VFD complicates things a bit because I don't know enough to know how it will affect the circuit, however that rise in voltage on your neutral may translate to a voltage between your "neutral" and any structure that is bonded to the general mass of the earth e.g. the structural steel of your shed or an earthed machine frame. Thus there is a risk of shocks and tingles. How much the voltage on the "neutral" could rise is determined by the magnitude of the out of balance load and the circuit impedance.

    A second issues arises if you are intending to use this to create a 415v 3 phase supply to several machines. How will you protect the individual circuits or will you rely on the VFD. The VFD can't see a fault to "neutral/earth" as anything other than an overload for faults past the autotransformer. Thus if you put yourself between a phase and neutral the result is likely a rather grim llama. I would check the fault loop impedance, after checking that your fault loop impedance meter will not place damaging loads onto the VFD in the process of testing.

    The transformer inductive impedance is a two edged sword. If load suddenly disappears from the secondary side of a transformer while the core is energised, the collapsing magnetic field will very likely induce high voltage spikes, not at all good for your VFD.

    I am actually very keen to hear how you go with this. I'm in a similar situation with the cost of 3 phase supply and this is an option I have been looking at.

    Cheers

    The Beryl Bloke
    Equipment er.... Projects I own

    Lathes - Sherline 4410 CNC
    Mills - Deckel FP2LB, Hardinge TM-UM, Sherline 2000 CNC.

  12. #12
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by Theberylbloke View Post
    I have thought of this setup in the past. I assume the VFD supplies 3 phases at 240 volts with no neutral? If I have that wrong please correct me.
    Correct.

    The transformer inductive impedance is a two edged sword. If load suddenly disappears from the secondary side of a transformer while the core is energised, the collapsing magnetic field will very likely induce high voltage spikes, not at all good for your VFD.
    That's what I was referring to in an emergency situation. Now I'm not sure if even turning the VFD off at the mains is a good idea as an emergency either.

  13. #13
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    3,228

    Default

    Any reason why you couldn't tie the neutral from the Y to the mains neutral?
    Chris

  14. #14
    Join Date
    Jul 2011
    Location
    Adelaide
    Posts
    837

    Default

    Quote Originally Posted by BobL View Post
    OK this is is unlikely to happen except in an emergency but I don't think the VFD will like it much as the transformer may not be able to protect the VFD.
    I am thinking of adding some circuitry to get around this possibility.

    Quote Originally Posted by BobL View Post
    Are you using any of the other features of the VFD?, eg speed and braking controls?
    No just simple V/F mode with acceleration at startup at a rate that stops the initial inrush from causing an over current fault.

    Quote Originally Posted by BobL View Post
    I can see it being useful on 415V delta machines with built in motors.
    I intend using it on a geared head drill with two speed motor and on my colchester bantam which also has a two speed motor.

    Quote Originally Posted by BobL View Post
    Does this mean you intend running more than one machine from the VFD? I would be be interested to see how that goes.
    I certainly do and like you I am interested to see what happens.

    I am currently working on a low pass filter between the VFD and the autotransformer.

  15. #15
    Join Date
    Jul 2011
    Location
    Adelaide
    Posts
    837

    Default

    Quote Originally Posted by Theberylbloke View Post
    I have thought of this setup in the past. I assume the VFD supplies 3 phases at 240 volts with no neutral? If I have that wrong please correct me.
    Correct.

    Quote Originally Posted by Theberylbloke View Post
    Your created "neutral" has no relationship to earth. A consequence is that any out of balance loading may cause a voltage rise on your "neutral". The VFD complicates things a bit because I don't know enough to know how it will affect the circuit, however that rise in voltage on your neutral may translate to a voltage between your "neutral" and any structure that is bonded to the general mass of the earth e.g. the structural steel of your shed or an earthed machine frame. Thus there is a risk of shocks and tingles. How much the voltage on the "neutral" could rise is determined by the magnitude of the out of balance load and the circuit impedance.
    Again correct.

    Quote Originally Posted by Theberylbloke View Post
    A second issues arises if you are intending to use this to create a 415v 3 phase supply to several machines. How will you protect the individual circuits or will you rely on the VFD. The VFD can't see a fault to "neutral/earth" as anything other than an overload for faults past the autotransformer.
    I will probably use an RCD downstream of the transformer.

    Quote Originally Posted by Theberylbloke View Post
    Thus if you put yourself between a phase and neutral the result is likely a rather grim llama. I would check the fault loop impedance, after checking that your fault loop impedance meter will not place damaging loads onto the VFD in the process of testing.
    Not the only way of becoming grim during this experiment. But I do thank you for your input. I have thought about the issue of voltage between earth and neutral and if I can't resolve it safely then I will simply do away with the feature and modify the one machine I have that utilises it.

    Quote Originally Posted by Theberylbloke View Post
    The transformer inductive impedance is a two edged sword. If load suddenly disappears from the secondary side of a transformer while the core is energised, the collapsing magnetic field will very likely induce high voltage spikes, not at all good for your VFD.
    The VFD should have back emf protection but I am not against using some judicially placed metal oxide varistors.


    Quote Originally Posted by Theberylbloke View Post
    I am actually very keen to hear how you go with this. I'm in a similar situation with the cost of 3 phase supply and this is an option I have been looking at.
    Thank you for the input it is good to have ideas kicked around a bit.

Page 1 of 2 12 LastLast

Similar Threads

  1. Replies: 0
    Last Post: 27th Jul 2018, 09:12 PM
  2. DONE: Single to three phase converter
    By Allan&glen in forum METALWORK - Machinery, Equipment, MARKET
    Replies: 10
    Last Post: 13th Oct 2012, 05:37 PM
  3. 240v single phase to 415v 3 phase conversion
    By Oldneweng in forum METALWORK GENERAL
    Replies: 81
    Last Post: 12th Jul 2012, 05:58 PM
  4. SOLD: vintage German made tool grinder 3 phase 240v &415v
    By thorens in forum METALWORK - Machinery, Equipment, MARKET
    Replies: 3
    Last Post: 4th Jul 2012, 10:11 PM
  5. 240V 1-phase to 415V 3-phase vfd
    By neksmerj in forum METALWORK GENERAL
    Replies: 23
    Last Post: 24th Dec 2010, 11:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •