25th Apr 2021, 11:18 AM #16Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 6,216
Cigweld stuff seems to be like that. Running a Cigweld transmig 250SE on my 15 amp supply and it will cut the flick down fuse after a short time running it at a high amperage. You might get a minute or two welding time out of it.
Upgrade to a 32 amp plug and the duty cycle improves considerably although the instantaneous output at the welder is unchanged.Gold, the colour of choice for the discerning person.
-
25th Apr 2021, 12:53 PM #17Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
Yes, the new imposed (lower) duty cycle seems to be an instruction to the user rather than something that would trigger a thermal or other overload of the machine. What it does trigger is the circuit breaker that is limiting the average current on the GPO.
It is strange that CIG would take the opportunity to fit a lower rated mains cord so that if you have (or upgrade to) a "proper" outlet, you need to upgrade the cord.
Your comments confirm that the machine itself (except for the power cord) is not changed in an Australian model - just the instructions. Thank you.
By the way, does the "colour of choice" relate to bullion or to TIG welding?
Jack
-
25th Apr 2021, 01:55 PM #18
It's funny that a power hungry machine will trip a 15A circuit, but work fine on a 32A.
There is some marketing tactic there for sure. The first thing people think when they see a single phase, 32A plug is "that's 3 phase". Proportionately fewer people have this in a home workshop. Which is where a 35-60A plasma would be used.
-
25th Apr 2021, 02:55 PM #19Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
And then the welder's power cord won't reach the power point so you need an extension cord. What's the difference between a 10 and a 15 amp extension cord - more insulation, the conductors are all 2.5 mm2 (assuming "heavy duty"). I don't know what a 25 or 32 amp extension cord looks like - I've never seen one.
Jack
-
25th Apr 2021, 06:53 PM #20
The circuit breaker protects the conductors. ie the wires.
The machine's over temp circuit protects it's conductors.
There are specs for what plugs need to be fitted to machines - namely the effective current (search my posts, I've spoken about this more times than I care to remember). These plugs need to be backed with suitable cross sectional area conductors for the machine side -IIRC 32A is a 4.0mm square CSA conductor. A standard home spec power cord is 1.5mm^2, a heavy duty extension lead cable is 2.5mm^2, so this is quite a bit bigger than a large extension cord.
The engineering controls then come into the equation per AS3000 which the sparkies adhere to- meaning that a circuit with a GPO on in needs to meet requirements for the cable size back to main circuit board, the size of conductors from main board to attachment point, and wires to the mains system (on the stobie pole), plus the voltage drop, number of cables in a conduit etc etc etc on premise.
This is so ham-fisted numpties don't (ie Can't- per design of the plugs and sockets) stick the wrong thing into the wrong outlet and put conductors at risk of melting and catching alight... where bad things can happen.
And if your power points are not close enough to where you want to use your machine... have a guess which trade you gonna call?
-
25th Apr 2021, 07:31 PM #21Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 6,216
-
25th Apr 2021, 07:45 PM #22
-
25th Apr 2021, 07:49 PM #23Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
Thanks for the summary but I don't have a problem with the regulations. My comment was really about what is easily available.
There is no difference between a 10 amp and a 15 amp GPO (aside from the sockets themselves) - the wiring is the same. The difference is in the number of GPOs that can be attached to the circuit (share a CB). A "heavy duty" 10 amp extension cord bought from the likes of Bunnings looks identical to a 15 amp extension cord except for the plugs and sockets.
I have not seen an extension cord for a 25 or 32 amp circuit - they are not sold at the likes of Bunnings or even the local tool shop. For the odd time that a welder cord might not reach a power outlet, I don't have a problem using an extension cord. There will be less loss extending the power cord than extending the work leads.
Of course, if I frequently had a problem where the welder cord didn't reach the outlet (in the same direction), I'd get another outlet fitted.
Regards
Jack
-
25th Apr 2021, 09:39 PM #24Diamond Member
- Join Date
- Mar 2014
- Location
- South of Adelaide
- Posts
- 1,225
We have a esab rebel on the boily ute at work, and we have been less than impressed with it. bought it to run off a genset for site work, and bought the recommended sized genset. turns out they are intolerant of any input voltage drop, after a few fried control boards, we now have to haul our 30kva genset around to use it. I was keen to get one for home, but not after the trouble we have had.
-
25th Apr 2021, 09:55 PM #25Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 6,216
https://www.ebay.com.au/itm/112235493309
Far cheaper to roll your own though. The parts are easily enough found.
I am going to get a 32 amp socket fitted to my shed when I get around to ringing an electrician.Gold, the colour of choice for the discerning person.
-
25th Apr 2021, 11:39 PM #26Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
Yes, a home made extension would be cheaper.
As the capabilities of some welders are being limited by the circuit breaker and GPO wiring, I wonder if there is a better option for a home workshop.
(I haven't checked so don't shoot me)
If a "domestic" 32 amp GPO were fitted instead of an industrial one, it would be compatible with 10 and 15 (and 25) amp plugs and therefore, the welders as supplied in Australia. Not particularly robust but very convenient.
I'd still be making an extra heavy duty extension cord.
Jack
-
25th Apr 2021, 11:47 PM #27Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
That's rather unfortunate. I don't have any experience running welders from a generator but I have heard that some mixes don't match.
Is it just the operation with the generator or are there other disappointments as well?
I'm not in a particular hurry so I'll keep listening to the experience of the group before I make a purchase.
Thanks for your input.
Jack
-
26th Apr 2021, 10:40 AM #28Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 6,216
I have not seen 240V sockets like that before.
Welders and plasma cutters off generators, you need a larger generator then you might think. My cut45 when measured with a amp meter actually puts out 50 amps and when the arc stretches out i measured 135 volts. (plasma cutters are constant current like a stick welder)
So 135 time 50 is 6750 watts output. Say an efficiency of 90%, that is an input wattage of 7500 watts. Or about 32 amps. Depending on how good the inverter design is, the really cheap ones are really crap, they only input power when the voltage is above a certain threshold as proven in my thread here https://metalworkforums.com/f309/t20...ator-waveforms
That is why some machines run absolute crap off a generator that should run them.Gold, the colour of choice for the discerning person.
-
26th Apr 2021, 01:19 PM #29Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
-
26th Apr 2021, 01:29 PM #30Senior Member
- Join Date
- Apr 2021
- Location
- Adelaide
- Posts
- 205
Similar Threads
-
Esab Compact 250 MIG $700 - Helensburgh NSW
By Chris Parks in forum METALWORK - Machinery, Equipment, MARKETReplies: 2Last Post: 29th Dec 2019, 03:39 PM -
ESAB tig torch consumables
By argeng in forum WELDINGReplies: 1Last Post: 14th Aug 2013, 09:07 PM -
esab c200i caddy mig
By Dobre in forum WELDINGReplies: 6Last Post: 14th Mar 2012, 01:11 PM -
esab
By pjt in forum WELDINGReplies: 17Last Post: 15th Oct 2009, 12:06 PM -
Is this an ok Welder - Esab LHN130
By prozac in forum WELDINGReplies: 2Last Post: 1st Mar 2009, 09:58 PM