  1. #61
    Join Date
    Apr 2021
    Location
    Adelaide
    Posts
    205

    Default

    I think the mains plug has been changed from at least 15 to 10 amps.

    In the US, as a rule of thumb:


    • A welder running on 208 – 230V primary requires a minimum breaker size of 30A with 50A recommend (this would be for welding at up to 180 amps).
    • Welding at an output of 200 amps or more requires at least a 50A breaker.


    In Australia we generally don't have 50 amp domestic circuits.

    (I'm not an electrician)

    Welding at 200 amps is probably about 4kW which translates to a mains current of about 17 amps. Taking power factor and efficiency into consideration and you are probably looking at 30 to 40 amps - say 40 amps (OK, no PFC and low efficiency).

    On modern welders, that 40 amps is called Imax. It is the current that would be drawn if you welded continuously and for that, you would need a breaker bigger than 40 amps.

    Another current, Ieff (the effective current) is the average current drawn based on the duty cycle of the welder. Attached is something from a BOC manual.

    On a modern welder, Ieff is approximately (Imax2 * DutyCycle)1/2

    = (402 * 0.3)1/2 = 22 amps

    So, assuming a 30% duty cycle, the 40 amp welder needs a 25 amp breaker (and circuit).

    If you exceed the duty cycle, eventually the breaker will pop.

    This is approximate and just for illustration but it shows why US welders when imported into Australia often have lower duty cycles listed in the manual.

    Jack
    Attached Images Attached Images

  2. #62
    Join Date
    Jan 2016
    Location
    Gosford
    Age
    63
    Posts
    173

    Default

    Thanks Jack. I felt it may be something to do with American 110V / 220V power supply but it doesn't explain why Caron says 15 Amp Circuit when everything else says 50. I'll have to watch his video again to see what he is saying.

    I found a sticker on the one I have that says it must not be connected to an outlet of less then 30 Amps and I'm assuming this is an Australian model. I have a 32 Amp circuit in my shed but it is only fitted with a 15 amp outlet. I'll need to look into a 30 amp outlet, plug and input cable. But then again I would never expect to run it at full 225 amp anyway, if at all.

    I wonder what it did to anything that tried to connect it to a 10 amp GPO.

  3. #63
    Join Date
    Dec 2018
    Location
    NSW
    Posts
    586

    Default

    Quote Originally Posted by Jack Ryan View Post
    On modern welders, that 40 amps is called Imax. It is the current that would be drawn if you welded continuously and for that, you would need a breaker bigger than 40 amps.

    Another current, Ieff (the effective current) is the average current drawn based on the duty cycle of the welder. Attached is something from a BOC manual.
    To add,
    Imax Is peak amperage (momentary, usually at arc initiation, or shortly after).
    Ieff Is average amperage at max machine load (consistent - ie what it will draw on full power, consistently)

    Not all circuit breakers are created equal, different trip curves (current and time), so in most cases a high Imax won't bother it, but a high Ieff will. This is where you can go to a D curve breaker which is abit more resilient to the high momentary Imax spikes, but still offer a suitable level of protection for a Ieff value within the design limit / current capacity of the conductor (aka your Wires).

  4. #64
    Join Date
    Apr 2021
    Location
    Adelaide
    Posts
    205

    Default

    Quote Originally Posted by glivo View Post
    Thanks Jack. I felt it may be something to do with American 110V / 220V power supply but it doesn't explain why Caron says 15 Amp Circuit when everything else says 50. I'll have to watch his video again to see what he is saying.
    I don't know the welder but I am thinking old transformer. That and 225 amps suggests that an outlet of more than 15 amps is required.


    I found a sticker on the one I have that says it must not be connected to an outlet of less then 30 Amps and I'm assuming this is an Australian model. I have a 32 Amp circuit in my shed but it is only fitted with a 15 amp outlet. I'll need to look into a 30 amp outlet, plug and input cable.
    Depending on how your shed is is wired, you may be able to get a 25 or 32 amp socket fitted with the current wiring from the main board. You'd have to ask an electrician - the trouble is, to do x, they may have to to y in preparation and before long you are getting a sub-station installed next door to feed your new house wiring and switchboard.


    But then again I would never expect to run it at full 225 amp anyway, if at all.
    You probably will.


    I wonder what it did to anything that tried to connect it to a 10 amp GPO.
    It depends what type, how old and how clean the wiring was. Terminal screws come loose, arc and get hot. The wiring is too small and would get warm - if it is buried in insulation, bird's nests and dust, it will get hotter still. Eventually, the evidence would be lost in the ensuing fire.

    A lot of people get away with swapping 15A plugs for 10A plugs - swapping a 25 or 32 amp plug for a 10 amp plug is seriously pushing your luck.

    Jack

  5. #65
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    429

    Default

    Remember, the typical american household voltage is 110/120 ish volts, that means on their supply a given task takes twice the current.

    Some of these welders are rewirable for different voltages, others contain a different transformer/choke.

    If a choke welder typically produces 120 amps welding current on Australian 240 volt supply it will typically be connected with a 15 amp plug, a 150 amp welder more like a 20 amp plug.
    If you do the math .. current and voltage, it does not add up because choke welders are very lossy.

    Modern inverter welders will produce a lot more welding current from a given supply and with a much smoother current profile.


    Remember none of this nominal current is real steady state current ..... it will peak way higher than the rated input and it's continuous current will probably be lower, particularly when the welding current is set below maximum output.

    In Australia we have 10, 15 and 20 amp standard 3 pin plugs without going to heavy industrial

    we have three core flex in 10 amp 1mm2, 15 amp flex in 1.5mm2 and 20 amp flex in 2.5mm2.

    If it is a heavy industrial welder it may require a 32, or 40 amp single phase plug or iut may run of two or three phases .... these plugs will look like nothing you will see in the home.


    WE DO NOT talk in wire guage. The whole American way of electrical though is different to Australian and the rest of the world.
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

  6. #66
    Join Date
    Apr 2021
    Location
    Adelaide
    Posts
    205

    Default

    Quote Originally Posted by soundman View Post
    Remember, the typical american household voltage is 110/120 ish volts, that means on their supply a given task takes twice the current.

    Some of these welders are rewirable for different voltages, others contain a different transformer/choke.

    If a choke welder typically produces 120 amps welding current on Australian 240 volt supply it will typically be connected with a 15 amp plug, a 150 amp welder more like a 20 amp plug.
    If you do the math .. current and voltage, it does not add up because choke welders are very lossy

    Remember none of this nominal current is real steady state current ..... it will peak way higher than the rated input and it's continuous current will probably be lower, particularly when the welding current is set below maximum output.
    Understood but this is a 220 volt welder. Most (better) American single phase welders operate on 110 or 220 volts but they are seriously rerated when operating on 110 volts.


    In Australia we have 10, 15 and 20 amp standard 3 pin plugs without going to heavy industrial

    we have three core flex in 10 amp 1mm2, 15 amp flex in 1.5mm2 and 20 amp flex in 2.5mm2.

    WE DO NOT talk in wire guage. The whole American way of electrical though is different to Australian and the rest of the world.
    The GPO wiring for 10 and 15 amps uses 2.5mm2 cable, 4 and 6 mm2 for higher currents. There are domestic 20, 25 and 32 amp three pin domestic GPOs that have L and C shaped earth pins. I would be interested to know if these can be fitted (by an electrician) in a DIY workshop rather than the industrial plugs that look like 3 phase plugs.

    Jack

  7. #67
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,216

    Default

    Quote Originally Posted by soundman View Post

    If it is a heavy industrial welder it may require a 32, or 40 amp single phase plug
    Never seen a 40 amp single phase plug. Although I see now EU 63 and 100 amp single phase plugs and sockets are for sale.
    Gold, the colour of choice for the discerning person.

  8. #68
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    429

    Default

    Quote Originally Posted by Jack Ryan View Post
    Understood but this is a 220 volt welder. Most (better) American single phase welders operate on 110 or 220 volts but they are seriously rerated when operating on 110 volts.




    The GPO wiring for 10 and 15 amps uses 2.5mm2 cable, 4 and 6 mm2 for higher currents. There are domestic 20, 25 and 32 amp three pin domestic GPOs that have L and C shaped earth pins. I would be interested to know if these can be fitted (by an electrician) in a DIY workshop rather than the industrial plugs that look like 3 phase plugs.

    Jack
    I was posting specifically about the flexes and plugs, that may be fitted to "appliances"

    Under current wiring rules and when fault loop impedance is considered. There is no specific wire cross section for any building wiring, 10 and 15 amp outlets may need to be wired in much heavier wire than 2.5mm2.

    Also consider that there may be multiple 10 amp outlets on a single circult, where where there are 15 and 20 amp outlets there can ( under most circumstances) be only 1 singe outlet on a circuit.

    As for those other plugs ...... they are not General Purpose Outlets and they are uncommon and in generally restricted to special application like "cooker plugs".

    Anything larger than a common 20 amp, 3 pin plug, particularly an industrial item should be fitted with an Industrial type plug, there are of course heavier flexes for industrial purposes.
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

  9. #69
    Join Date
    Jan 2016
    Location
    Gosford
    Age
    63
    Posts
    173

    Default

    I will have to look more closely at the machine to determine the exact model and if it was made (labelled) for Australian use. These things are as common as hotdogs in the states. Every man, boy and dog has one and they now come in 2 versions. AC 225 and more recently the AC 225 DC 125. Many videos exist of people restoring old ones and putting bridge rectifiers in the AC ones to make a bastardised DC welder. Google it or do some youtube searches. There are plenty of clowns showing them off and doing stuff with them. Amusing to say the least. Americans can be funny sometimes.

    If this unit was sold in Australia and requires a minimum 30 amp circuit, then I don't know many places that would have that circuitry built into their sheds. They can be run off a single phase from a 3 phase circuit (apparently). I don't know anything about these units being translated into Australian use, which is why I've asked if anybody knows of them over here. I now have one.

    I just see a big mismatch in the size of the input cable and the rated input specs. Something doesn't sit right. To be honest the input power cable looks original and there would be no way it is capable of 30 amps. 15 or 20 max.

    I inherited this welder during a bizarre situation that needs not be discussed here, but I recognised what it was and decided to bring it home for the novelty (with another 2 stick welders that are a different topic again). I have not seen them in Australia before this one but they are all over USA. They weigh about 50 kg or more and are a big multi-tapped iron core transformer with a fan and a selector switch in a red box that looks like a tombstone.

    Edit; Just re-watched the Kevin Caron video on replay a few times. He is saying "220 Volt 50 Amp circuit breaker".

    Added: Well it would seem that to wire this into a power supply would require 4 mm cable (3 core t&e) and a 32 Amp round 3 round pin outlet socket and plug. I have 4 mm wiring to a single dedicated outlet but it is only fitted with a 15 amp flat pin outlet for my modern welders. I will have a look at the size of the wire on the existing input cable. I doubt it is 4 mm with a 10 amp plug but I'll have a look.

  10. #70
    Join Date
    Jan 2016
    Location
    Gosford
    Age
    63
    Posts
    173

    Default

    Well, if anybody is interested, this unit is built in Australia by Lincoln Australia. It has a NSW Energy certification plate and also one that says it complies with Australian Standards, 1966, whatever that is. I'm assuming it is the standards from the year 1966. My preliminary investigation shows that, as I thought, the input cable is actually original. It is 4 sq mm cable and it is actually tinned copper multi-strand wire, and it's in good condition still. I think this welder has been sat in a shed somewhere.

    Some idiot has long ago fitted a 15 amp plug and then filed the earth pin down to fit a 10 amp GPO. It was most likely rendered unusable at that point so it has probably been unused for most of it's life. This plug is no longer there. It never ceases to amaze me what some people will do, and surprisingly not burn the shed down or electrocute themselves.

    The stickers and plates on it say to not connect to a power supply rated at under 30 amps and also that the input amperage is 26 amps at 250 volts. I'm old enough to remember 250 volts, but I think we are now 240 volts supply on a good day.

    The collectable value is that it is in really good condition, with probably very little use and it still has the protective removable plastic on the main dial plate. Just like my 30 year old Fender scratch plate. The paint job is still in fair condition but it has sat on dirt floor at some point. It is fitted with the Lincoln accessory wheel kit and the work leads and attachments appear to be original as well. Do you leave it original or replace with more serviceable items?

    These things are all over the USA. I wonder how many exist in Australia.

    I watched one video where a guy tried to scrap one and then advised against it as the transformer windings are aluminium strips and the units contains hardly any copper. Probably why the price point in the states is so low still even today.

  11. #71
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,216

    Default

    The 225 amp lincoln tombstone welder I have seen has a 32 amp plug.
    Gold, the colour of choice for the discerning person.

  12. #72
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    3,228

    Default

    Quote Originally Posted by glivo View Post
    They can be run off a single phase from a 3 phase circuit (apparently).
    I thought a three phase breaker will pop if there’s a significant phase imbalance?
    Chris

  13. #73
    Join Date
    Jan 2016
    Location
    Gosford
    Age
    63
    Posts
    173

    Default

    Quote Originally Posted by jack620 View Post
    I thought a three phase breaker will pop if there’s a significant phase imbalance?
    You're probably right. Maybe this is possible in the States. I don't know. I think I read it in the American user manual.

    Sent from my SGP521 using Tapatalk

  14. #74
    Join Date
    Mar 2014
    Location
    South of Adelaide
    Posts
    1,225

    Default

    Quote Originally Posted by jack620 View Post
    I thought a three phase breaker will pop if there’s a significant phase imbalance?
    don't think so, my 3 phase tig and stick welders only use 2 phases.

  15. #75
    Join Date
    Nov 2016
    Location
    Gulfview Heights, Adelaide
    Posts
    83

    Default

    In summary, in Australia, this Lincoln welder should run from a 32 amp rated supply on single phase ( 240 volts).

    Paul.

Page 5 of 6 FirstFirst 123456 LastLast

Similar Threads

  1. Sparky patch lead question
    By Legion in forum WELDING
    Replies: 8
    Last Post: 19th May 2014, 09:18 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •