Originally Posted by
HattyDamp
Hi...i am a new user here. I design electrical systems for industrial installations and I'm not clear on how to size a feeder for a control panel containing multiple VFD's. If I consider that control panel to be an Adjustable-Speed Drive System, 430.122 says Branch/Feeder conductors must be sized 125% of the input current of the power conversion equipment. Does that mean I need to add up the total VFD input current and add 25% for the feeder size?
If I consider the control panel to be an Industrial Control Panel, 409.20 says the supply conductor must be sized for 125% of the full-load current of the largest motor plus the sum of the full-load current of all other motors. There's no mention here of VFD's or sizing the conductor based on VFD input current rather than motor full-load current.This gets to be an issue where a panel shop puts several over-sized drives in a panel. I recently had a project where there were 15 VFD's in a panel serving 1HP - 5HP motors, and the shop put in all 7.5HP drives.