    Default 3ph motor/VFD no torque

    I'm probably doing something stupid/obviously wrong, however:

    I bought a drill press that had been installed on a fixed/hardwired 3ph line. Motor is a GMF, plated 400/440V, 1.2A, 0.5HP, 1400rpm, 3ph continuous duty. I hooked it up to a 2 horse rated 240V VFD, dialed in all the parameters for a 50hz motor, and the motor runs at its rated speed, but has f-all torque. Motor appears to be delta. I can rub a bit of timber against the rim of the main pulley and stall it.

    Am I missing something here? This formula has worked on my other 3ph conversions, I feel like I must be missing something really obvious.

    Also, related: Every time I've done a 3ph->1ph conversion, I've noticed that the tool suddenly needs chassis grounding - in the case of this drill press, despite being grounded to the motor casing, touching the tool body anywhere when the motor is running will give you a mild AC shock, until the tool body has a separate ground added to it. I must be missing something, again, really obvious, because it doesn't make sense to me - the motor body is conductively connected to the rest of the tool, surely the case ground should also ground the rest of the tool? If I'm getting a shock off it, why isn't it tripping the RCD?

  2. #2
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,189

    Default

    If its a 400/440 V Delta OR Star it will only output 0.25hp at 240V.

    The motor has to be configurable to 240V DELTA to output its full power..

    If it doesn't say it can be done on motor name plate then it cannot usually be done just in the motor junction box.

    If it is a 440.440V delta then you are SOOL.
    If it is a 400/440V Star it may be configurable to 240V delta by a motor rewinder or someone who knows how to did out the common point and make the connections.

  3. #3
    Join Date
    Feb 2016
    Location
    NSW
    Posts
    117

    Default

    Well, I'm SOL. That was silly of me. Thanks Bob.

    Guess I'll wait for a cheap foot mount 3ph fractional motor to pop its head up.

  4. #4
    Join Date
    Jan 2011
    Location
    Far West Wimmera
    Age
    63
    Posts
    4,049

    Default

    Do you get a shock when you touch the motor?

    If you get one from the drill press and not the motor then this would indicate that they are not connected properly. Connect them together with a jumper lead and see what happens. I would think that all machines should be grounded seperately from the motor.

    Dean

  5. #5
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    3,228

    Default

    Quote Originally Posted by Precious Mettle View Post
    the motor body is conductively connected to the rest of the tool,
    Are you sure it is? If adding a separate earth solves the problem I suspect the motor to chassis bonding isn't effective.

    Quote Originally Posted by Precious Mettle View Post
    If I'm getting a shock off it, why isn't it tripping the RCD?
    The fault current may not be exceeding the 30mA trip current of the RCD.
    Chris

  6. #6
    Join Date
    Jul 2006
    Location
    Athelstone, SA 5076
    Posts
    4,258

    Default

    I would'nt be using it if you get a shock...no matter what!!!
    something is wrong..get a sparkie or someone who knows what they're doing to check it out

  7. #7
    Join Date
    Jun 2008
    Location
    The Whitsundays
    Posts
    229

    Default Shocks

    Quote Originally Posted by Precious Mettle View Post
    Also, related: Every time I've done a 3ph->1ph conversion, I've noticed that the tool suddenly needs chassis grounding - in the case of this drill press, despite being grounded to the motor casing, touching the tool body anywhere when the motor is running will give you a mild AC shock, until the tool body has a separate ground added to it. I must be missing something, again, really obvious, because it doesn't make sense to me - the motor body is conductively connected to the rest of the tool, surely the case ground should also ground the rest of the tool? If I'm getting a shock off it, why isn't it tripping the RCD?
    There are any number of reasons why you might get a shock. I have investigated quite a few shocks. I strongly suggest you contact a good elecrician and get them to come around and do some testing for you. Alternatively, your supply authority might be charged under legislation with such investigations and your electrician may well refer you to them.

    When was the last time you tested your RCD? are you sure that it works? I seem to recall that they should be operated by the test button every 3 months?

    Cheers

    The Beryl Bloke
    Equipment er.... Projects I own

    Lathes - Sherline 4410 CNC
    Mills - Deckel FP2LB, Hardinge TM-UM, Sherline 2000 CNC.

Similar Threads

  1. Imperial and Metric Bolt Thread and Torque Chart
    By moorebrm in forum METALWORK GENERAL
    Replies: 5
    Last Post: 31st May 2016, 01:48 AM
  2. Printable imperial-metric-bolt-thread-torque-chart
    By moorebrm in forum CONVERSIONS & CALCULATIONS
    Replies: 0
    Last Post: 16th May 2016, 09:03 PM
  3. Nut/bolt torque figures
    By morrisman in forum METALWORK GENERAL
    Replies: 7
    Last Post: 23rd Feb 2015, 02:09 PM
  4. Preventing collet slip & tool holder torque
    By steran50 in forum METALWORK GENERAL
    Replies: 15
    Last Post: 8th May 2013, 02:57 PM
  5. Replies: 21
    Last Post: 21st Mar 2013, 05:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •