    Hi Chris,
    Thanks for that, at least some of that makes sense.
    I guess the first thing to check is if the A on the VSD and the meter are even close. Which it sounds like there is a good chance they wont be.

    Even if I could get comparative measurements, that might be a start.

    Stuart

  2. #17
    Join Date
    Aug 2007
    Location
    Melbourne
    Age
    68
    Posts
    1,410

    Default

    Quote Originally Posted by Stustoys View Post
    Even if I could get comparative measurements, that might be a start.
    Just keep it safe, we do not want to loose you. It is too easy to forget, that one is measuring on unforgiving power electronics.

  3. #18
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    5,080

    Default

    Quote Originally Posted by Stustoys View Post
    Hi Chris,
    Thanks for that, at least some of that makes sense.
    I guess the first thing to check is if the A on the VSD and the meter are even close. Which it sounds like there is a good chance they wont be.

    Even if I could get comparative measurements, that might be a start.

    Stuart
    Hi Stuart,

    You can increase the sensitivity of the CT by wrapping another turn through the toriod.

    Ray

  4. #19
    Join Date
    Jun 2008
    Location
    The Whitsundays
    Posts
    229

    Default ring around the rosie, er I mean coil

    Hi Stu,

    You can loop the primary through the coil as many times as you like. Naturally two loops doubles your reading in the secondary.

    It may not be obvious to everyone that you only loop the active through the coil and not say the active and neutral together as the induction in that case will cancel out and give you nothing.

    Cheers

    The BerylBloke

    Quote Originally Posted by Stustoys View Post
    So am I allowed to do a 180 around the coil? I cant see why not.........

    Hi Chris,
    I'm pretty sure the Teco only displays Hz(though I'm not game to try and measure the V on the 415V with that gauge, that might be pushing things). The cheap ones have A.

    I'd been wondering what the PWM would do to the amp meter(and the V for that matter)
    I have an anolog meter, would that average enough?
    I have a scope but wouldnt the vsd or the scope need to be isolated? Cant imagine me being able to calculate area of signal.


    Hi Bob,
    I tested the gauge against a DMM on my variac.
    Gauge mains% DMM

    253 100% 249
    192 75% 188
    129 50% 125
    106 40% 101
    81 30% 76
    68 25% 63
    57 20% 50
    52 15% 39
    45 10% 26
    39 7% 17 (just above the gauge turn off V)(didnt change range on the DMM)

    So it seems pretty good down to 60V(of course it might let the smoke out after 5 minutes)


    Stuart
    Equipment er.... Projects I own

    Lathes - Sherline 4410 CNC
    Mills - Deckel FP2LB, Hardinge TM-UM, Sherline 2000 CNC.

  5. #20
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,188

    Default

    Thanks for the info on the meters.
    I might go out to the Uni and see if I can borrow a up market meter to cross check my DMM and the little V/I panel meter.

  6. #21
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    Quote Originally Posted by cba_melbourne View Post
    Just keep it safe,
    Yes, as this will be running for much more time than any normal bench test I'm double insulating everything like its a permanent installation. I might end up letting the smoke out of something but as long as it isnt me or the Teco I'll be happy.
    Though I was more worried about the drum coming apart. Even though I was "pretty sure" it would be ok I was standing 10ft away behind my mill... just in case. I make it about 250kph at 2800rpm........though the loads and temps arent the same.

    Quote Originally Posted by RayG View Post
    You can increase the sensitivity of the CT by wrapping another turn through the toriod.
    Hi Ray,

    Wont that double the amps displayed?(granted not a huge mathematical challenge)

    Stuart

  7. #22
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    5,080

    Default

    Quote Originally Posted by Stustoys View Post

    Hi Ray,

    Wont that double the amps displayed?(granted not a huge mathematical challenge)

    Stuart
    There's a pot for calibrating the amps, and another for calibrating the volts. Just wind it back to match the NIST certified DVM

    The data sheet I looked at says that the amp range is 0-50A, since I figure that you'll be down below 10A for most of the measurements, you'd get better results by changing the range to 0-25A..

    The mechanical stability of the CT is important and wrapping a turn around the toroid makes it more stable mechanically as well.

    Ray

  8. #23
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    Quote Originally Posted by RayG View Post
    You can increase the sensitivity of the CT by wrapping another turn through the toriod.
    Do you think that would improve the accuracy of the current readings?

    Quote Originally Posted by Stustoys View Post
    Wont that double the amps displayed?(granted not a huge mathematical challenge)
    Quote Originally Posted by Theberylbloke View Post
    You can loop the primary through the coil as many times as you like. Naturally two loops doubles your reading in the secondary.
    Thank you tbb, I'll take that as a yes. Damn I type slow when I'm trying to get three things done at once.

    Stuart

  9. #24
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    Quote Originally Posted by RayG View Post
    There's a pot for calibrating the amps, and another for calibrating the volts. Just wind it back to match the NIST certified DVM

    The data sheet I looked at says that the amp range is 0-50A, since I figure that you'll be down below 10A for most of the measurements, you'd get better results by changing the range to 0-25A..

    The mechanical stability of the CT is important and wrapping a turn around the toroid makes it more stable mechanically as well.

    Ray
    There is? I had better take a look. At least they will all be the same

    So would a cable ties and a little hot melt glue to hold things in place be a good idea?

    Stuart

  10. #25
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    5,080

    Default

    Quote Originally Posted by Stustoys View Post
    There is? I had better take a look. At least they will all be the same

    So would a cable ties and a little hot melt glue to hold things in place be a good idea?

    Stuart
    Just cable ties would do.

    The one I got, is a model DDH-303L and the pots are accessible through holes in the top PCB.. I'd use a plastic alignment tool, and be careful, there's 240V terminals not far away from the Voltage calibration pot.

    Ray

  11. #26
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,188

    Default

    For ease of connectivity and safety I made up a pair of 3 phase leads, one to connect the VFD to a high current terminal strip inside a transparent plastic box, and then the other lead connects the motor to the terminal strip.

    The connections to the VFD and the motor are via soldered ring terminal crimp connectors, while the terminal box has with proper cable glands in the sides, so everything is robust and secure.

    Using a break out box has a number of advantages such as, I'm not constantly connecting and disconnecting wires inside the VFD, I can also test V/A at the terminal box without needing to poke probes into the VFD or at the motor end so I can leave these safely covered and the only thing exposed is the terminal box - for testing over time, I can also screw the cover over the terminal box.

    When I finish I leave the terminal box connected to the VFD for testing other motors, and pack the whole lot away in a plastic tool case.

  12. #27
    Join Date
    Jun 2008
    Location
    The Whitsundays
    Posts
    229

    Default Ammeter Accuracy

    Hi Stu,

    If this is a digital meter then I'd put as many turns on the primary as required to get the reading towards the top of the ammeter's range. That way, after taking your multiplier into account, each bit will equate to less primary current and should give you greater "accuracy". I use the term loosely as I'm not sure of the toroid's behaviour at other than design frequencies, likely 50 hz? Also what is the the toroid's original use as that will affect it's accuracy? It's been many years since I played with metering transformers, for some reason the term "saturation" comes to mind??

    Cheers

    The Beryl Bloke
    Quote Originally Posted by Stustoys View Post
    Do you think that would improve the accuracy of the current readings?





    Thank you tbb, I'll take that as a yes. Damn I type slow when I'm trying to get three things done at once.

    Stuart
    Equipment er.... Projects I own

    Lathes - Sherline 4410 CNC
    Mills - Deckel FP2LB, Hardinge TM-UM, Sherline 2000 CNC.

  13. #28
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    These VSD's are setup with 3 phase plugs and sockets. I was planning on making the connections inside the plug, but I spare plugs, sockets and boxes, maybe that would be a better way to go. I'll have a look tomorrow.

    Stuart

  14. #29
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,188

    Default

    Quote Originally Posted by Stustoys View Post
    These VSD's are setup with 3 phase plugs and sockets. I was planning on making the connections inside the plug, but I spare plugs, sockets and boxes, maybe that would be a better way to go. I'll have a look tomorrow.
    I also originally used 16A 3Phase plugs and sockets but given that the 3HP or less motor currents (while quite lethal!) are not that high I decide to go with a chunky break out box. I use soldered ring terminal crimp connectors where I can and solder the ends of all bare wires, triple check the connectors are snug and tight. I am sometimes able to borrow a Megger testing unit from work but now that everyone is back at work I have to take stuff out there for testing.

    I see there are a lot of cheap Megger testing units on ebay these days - anyone have any experience with those?
    Yep I do know that a megger shouldn't be used with a VFD in the circuit but at least it can be used to check out the wiring and motor etc before the VFD is connected.


  15. #30
    Join Date
    Oct 2011
    Location
    Norwood-ish, Adelaide
    Age
    59
    Posts
    6,559

    Default

    Quote Originally Posted by BobL View Post
    I see there are a lot of cheap Megger testing units on ebay these days - anyone have any experience with those?
    I bought one when I got my mill - I figured I should test things before discovering the casting was live the hard way.
    It seems to work. It said no shorts and there were not any but I've never had a fault condition with a real megger that I could compare with.

    Michael

Page 2 of 16 FirstFirst 123456712 ... LastLast

Similar Threads

  1. Welder tests
    By Grahame Collins in forum WELDING
    Replies: 3
    Last Post: 28th May 2008, 11:56 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •