3ph VFD for 3kW mill spindle motor
Since I'm a VFD virgin, I'm after a sanity check of my plans to install a VFD on the spindle motor of a 1980's TOS mill.
The mill has quite a bit of electrical control. 5 motors (spindle, feed, coolant and 2x lube motors) as well as control for rapid traverse and a supply for the DRO. The electrical cabinet resembles something from the space shuttle. Complexity is low, there's just lots of of it!
I'm trying to make it home friendly with the least modification. I don't have 3-phase at home, but have a decent size rotary phase converter that should be good for over 5HP so have decided to just supply the mill completely off the RPC but use a 415v 3ph VFD for the spindle motor.
I've got access to mains 3ph at work so the plan is to get modified and tested on a known good power source before it goes home.
Main reasons for fitting the VFD are:
- to soften the load on the RPC when the spindle starts
- speed control (max spindle speed is 2000rpm standard. A 50% increase on that - 3000rpm - would be nice)
- possibly some braking/deceleration control
So I think I'm after a 3kW 415v 3ph ==> 415v 3ph inverter with a remote control panel to mount on the existing mill control console (keeping the high voltage power stuff in the electrical cabinet/VFD).
The cable from the inverter to the remote panel would need to be about 2m long so I'm thinking it has to be a CATV style cable or similar rather than the ribbon style.
Would need the ability to add a braking resistor if required, and definitely will also need to do forward and reverse and jog (which I assume is all pretty standard).
Does that sound reasonable?
I'm keen to give one of the Powtran units a go since BobL has given them a good rap and others seem to be having success with them, but a bit confused by their huge range. The particular ones that have been recommended previously in the forum are typically 1ph to 3ph.
Looks like their PI500A model might be suitable for what I need, but I could be way off the mark so any guidance there would be appreciated too.
Steve
-
18th Feb 2019, 11:37 PM #2Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
One problem you might have is that Powtran don't seem to make a 3kW VFD - they seem to jump from 2.2 to 4kW on all their model ranges.
I have been trying to get a copy of the english manual for their 500 series VFDs for a few months without any luck. I think they are still away on chinese new year holidays so maybe wait a few days before trying to contact them.
-
19th Feb 2019, 07:39 AM #3Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
Thanks Bob. I'm not in a hurry - have plenty of other projects on the go so will leave it until next week to contact them.
Although practically I'd probably get away with a 2.2, I'll get a 4kW model.
Steve
-
19th Feb 2019, 11:39 AM #4Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
Having a look through the other Powtran models in the meantime. Have a few more questions:
Download links for the manuals etc on the website don't seem to work. Are the links just broken or do you need to be registered to access them?
Is there a particular terminology they use for the CatV style remote cable so I can make sure it has that style?
Input voltage: My RPC is ~400v output but runs quite unbalanced unloaded and may be up around 440v P-P. Is a VFD going to cope with that or is it likely to trigger an overvoltage situation? Possibly it depends on the particular inverter capability which brings me onto....
There seems to be a bit of variation in the input voltage specs for the different 3ph input models.
The PI500A for example is listed as 380v(-15%)-440v(+10%), but the PI160 is 380v (+-10%). On the face of it the PI160 wouldn't be suitable. Is it that simple or is there a bit of Chinglish interpretation in the specs.
Steve
-
19th Feb 2019, 12:23 PM #5Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Their website links have never all been completed - we need to keep in mind that they are not a retail business. They sell VFDs by the container load so they don't particularly care about one of a kind sales.
Is there a particular terminology they use for the CatV style remote cable so I can make sure it has that style?
Input voltage: My RPC is ~400v output but runs quite unbalanced unloaded and may be up around 440v P-P. Is a VFD going to cope with that or is it likely to trigger an overvoltage situation? Possibly it depends on the particular inverter capability which brings me onto....
There seems to be a bit of variation in the input voltage specs for the different 3ph input models.
The PI500A for example is listed as 380v(-15%)-440v(+10%), but the PI160 is 380v (+-10%). On the face of it the PI160 wouldn't be suitable. Is it that simple or is there a bit of Chinglish interpretation in the specs.
All my HY VFD's are listed a 220V +/- 10% so 242V is the supposed max. I have panel meters all over the place in my shed so I can see what the mains V is and its almost always over 240V and I often see 248V and even 250V here - some of these VFDs are now 7 years old and still working well.
-
19th Feb 2019, 03:07 PM #6
Just a quick note about the imbalance of your RPC: the inverter doesn't care at all about that. It rectifies whatever you feed it into a single DC voltage and current anyway. It then chops it into 3-phase sinusoidal AC with controllable/variable frequency. The output will be well-balanced.
Cheers, Joe
retired - less energy, more time to contemplate projects and more shed time....
-
19th Feb 2019, 03:23 PM #7Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
-
19th Feb 2019, 05:38 PM #8
Not so sure about imbalaced supplies Joe. The input stage is going to be a three phase rectifier in some form. Any rectifier will only conduct current when the instantaneous input voltage applied is greater than the instantaneous voltage of the storage capacitors connected at its output. If the phases are badly imbalanced, the highest voltage phase will conduct for a significantly longer portion of the cycle than for the lower voltage phases. It is quite possible that the lowest voltage phase may never conduct. For the VFD to function properly, the diodes for the highest voltage phase may be seriously overloaded (current and thermally), while those for the other phases are underworked. This could lead to premature failure of the VFD, depending on how much headroom there is in the rectifier specifications.
A lot of the 220-240V input VFD's utilise a three phase input stage that is also compatible with single phase supplies, suggesting that the rectifier block in them has sufficient overhead to cope with all of the supply power being derived from a single phase. In a 380-415V input VFD, the designers may anticipate that the unit would not be subjected to a significantly imbalanced three phase or 380-415V single phase supply, and may not allow the headroom to cater for such in the rectifier block. I note that many supplier offer specific models for use with 480V SWER derived supplies, presumably because they have a single phase rectifier block designed to cope with the higher currents and thermal loads that a single phase input imposes. Being a sceptic, I suspect that they do this because they don't have confidence that the equivalent 380-415V three phase input units would cope well with the effective imbalance that the 480V SWER derived supply represents. Then it comes down to just how tolerant are the rectifier stages of the VFD, and how imbalanced is the output from the RPC. The only effective way to tell is to buy the unit, commission it, and use it. If it has a usable lifespan, then the variables are in your favour, it it dies prematurely, then they were not.
I do not dispute the argument that VFD with an imbalaced input should produce a well balanced three phase output, just point out that the selection of the components in the rectifier block may have a significant impact on the reliability of the system when faced with significantly imbalanced supplies and loadings approaching the devices ratings. One reasonable approach to overcoming the issue may be to to derate the VFD, i.e buy and use a VFD capable of handling a load twice that likely to be imposed, to ensure that the rectifier can handle the increased peak currents and power associated with the imbalanced supply.I used to be an engineer, I'm not an engineer any more, but on the really good days I can remember when I was.
-
19th Feb 2019, 06:47 PM #9Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
IIRC, going back a few years when 1ph-3ph VFD's weren't so commonplace, it was standard practice to just use a 3p-3p unit of double the power rating and run it off a single phase.
Steve
-
20th Feb 2019, 02:18 PM #10
At moderate power ratings where the rectifier block probably can handle all of the input current coming from a single phase, you may not even have to allow for derating to half rated power out, though it is a good rule of thumb for higher powered units.
The issue with cheaper VFD units is that normally the output voltage is limited to the input voltage, so 240V in generally means 240V 3ph out, which in turn means motors max out at 50% rated power, need to be reconfigured for a different winding connection or need to be rewound/replaced to achieve maximum output. There are some exceptions that can make 415V 3ph from 240V single phase input by use of a different voltage boosting input stage. The more commonly available units were based on Asian VFD's and modified, available from the UK but were more than twice the price of the units they were based upon, and from memory limited to about 2KW output. I am not familiar with the Powtran offerings, so I don't know if the stepup VFD situation has improved any.I used to be an engineer, I'm not an engineer any more, but on the really good days I can remember when I was.
-
24th Feb 2019, 10:44 AM #11Member
- Join Date
- Feb 2012
- Location
- Sydney
- Posts
- 67
Alternate sites for PowTran Manuals
Steve, I found the same problem trying to download Powtran manuals but found them on alternate sites simply by googling e.g. "Powtran PI9000 Manual". Here's one site that I found but there are numerous others: https://www.manualslib.com/manual/1192464/Powtran-Pi9000-Series.html#manual
-
25th Feb 2019, 06:24 PM #12Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
-
25th Feb 2019, 11:28 PM #13Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
-
13th Mar 2019, 03:44 PM #14Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
The VFD just arrived. Well packed and labeled and in good condition.
Much smaller than I expected though.
The plug on the removable control module is RJ45 which makes it nice and easy to extend.
Steve
-
9th May 2019, 05:07 PM #15Most Valued Member
- Join Date
- Nov 2017
- Location
- Geelong, Australia
- Age
- 57
- Posts
- 2,666
Finally had a chance to do some basic settings and hook up the VFD temporarily for testing. Running on real 3-phase supply in the workshop at work for testing, so I know its OK before attempting to run it from my RPC at home.
Started by leaving it at the default 50Hz max frequency, and 10sec accel/decel setting. Starts and stops nicely (but obviously very slowly). I can decrease the speed by winding the pot back on the control panel.
Positive first steps
I'll need to be able to run it in reverse, and it would be nice to be able to jog - but can't see a logical way of commanding either of those via the control panel.
How are those things normally done? Set up some form of simple external switch arrangement and find the appropriate terminals in the VFD to connect to or is there a better way?
Steve
Similar Threads
-
MMD-45 Mill Tight Spindle
By Oldneweng in forum METALWORK GENERALReplies: 39Last Post: 24th Oct 2014, 05:54 PM -
High Speed Spindle for the Mill
By RayG in forum METALWORK GENERALReplies: 10Last Post: 11th Sep 2012, 02:44 AM -
Where to buy DM45/46 Mill with R8 spindle?
By variant22 in forum METALWORK GENERALReplies: 16Last Post: 27th Aug 2012, 11:01 PM -
Need Some Advice: Level up Spindle on HM-46 Mill
By Jarh73 in forum METALWORK GENERALReplies: 9Last Post: 19th Apr 2011, 02:45 PM -
Mill Spindle Bearing Grease
By markjaffa in forum METALWORK GENERALReplies: 12Last Post: 7th Jun 2010, 11:51 AM