    The nuisance trip from RCD's can occur frequently. One solution is a time delayed RCD. These RCD's cost substantially more than your common RCD, but allow a small time when connected for the caps to charge in the RCD before they allow normal operation. They then behave exactly the same as a normal 30mA RCD.

  2. #17
    Join Date
    Nov 2010
    Location
    Frankston south
    Posts
    102

    Default

    Not all vfd's trip rcd's. I have some Mitsubishi inverters that are fine, and some SEW's that are not.

  3. #18
    Join Date
    Aug 2006
    Location
    Melbourne
    Posts
    1,105

    Default

    What is causing them to trip though? Could just be something as simple as a setting.

  4. #19
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    915

    Default

    I would have thought that ANY earth leakage from ANY piece of electrical equipment is an issue that should be resolved.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  5. #20
    Join Date
    Jan 2004
    Location
    Mackay North Qld
    Posts
    6,446

    Default

    The geckos in my shed get inside the gpo's and obviously short the switches. Until recently it was not a problem,
    With a second freezer in there now, I have to check the RCDs every morning otherwise I may have a freezer full of bad meat.

    The ants do a good good job of removing the zapped geckos but I do wonder can the switched gpo,s be sealed up without any detriment to them?

    The odd thing is that it does not happen inside the house. We don't see geckos inside the house. Maybe they don't like the aircon.

    Grahame

  6. #21
    Join Date
    Aug 2008
    Location
    Perth
    Posts
    26

    Default

    The vfd's can cause the RCD's to trip through a couple of different means. Either by the charging of the internal capacitor bank or some vfd's contain filter circuit to minimise electrical noise on the circuit it is attached to. Neither of these occurrences can harm the operator, just creates an imbalance in the active/neutral lines and trips the rcd.

  7. #22
    BobL is offline Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by Grahame Collins View Post
    The ants do a good good job of removing the zapped geckos but I do wonder can the switched gpo,s be sealed up without any detriment to them?
    Yes they can be sealed.

    Many years ago (pre RCD days) I was having breakfast when one of the 20A (non-RCD) house circuits tripped.
    After some fruitless investigations inside the house I remembered that the same circuit also went down to the shed and when I threw open the shed door I was hit with the smell of acrid smoke and saw one of the GPOs under the window was smouldering and looking like it was about to catch fire.

    What I worked out happened was ants had setup a nest inside the GPO.
    This was pre-dust serious collection days and the GPO was also partially buried in sawdust which I guess made it nice and warm inside the GPO.
    During a storm in the night, a small amount of rain had blown in under a window and entered the GPO such that the mix of water, fine sawdust and ant juice (formic acid) shorted the inside of the GPO.
    So although the power was off the GPO and sawdust around it was still smouldering and developing into a proper fire - luckily some of the sawdust was also damp from the rain.
    The inside of the GPO got hot enough to melt the insulation around the wires so they had touched each other causing the breaker to open.

    That's when I decided to have RCDs adde to the house circuits, installed a sealed window in the shed and it became a driver to get some proper dust collection going.
    An RCD would have switched the circuit off much earlier but just in case I also installed a fire alarm.

  8. #23
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    915

    Default

    Quote Originally Posted by benhoskin View Post
    The vfd's can cause the RCD's to trip through a couple of different means. Either by the charging of the internal capacitor bank or some vfd's contain filter circuit to minimise electrical noise on the circuit it is attached to. Neither of these occurrences can harm the operator, just creates an imbalance in the active/neutral lines and trips the rcd.
    I'm not saying that it doesn't happen, only that it shouldn't. I would suggest that that behavior is not "normal" and is caused by a faulty device (maybe only a "slightly faulty") or poor design.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  9. #24
    Join Date
    Aug 2008
    Location
    Perth
    Posts
    26

    Default

    The fault is not a problem with the device.It is just caused by certain devices in normal operation.As long as that is what is causig the RCD to trip and not another wiring problem. Ideally it would not happen, and there is a solution, the time delayed RCD's, but not many people would like to pay for them. A three phase 32 amp rcd/breaker delay combo is ~$400 just for the part. It is actually not a bad thing if you do get the tripping. It makes you operate the RCD, this ensures that the trip mechanism is actually working and not stuck.

  10. #25
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    9,088

    Default

    The only issues I've had with old machines that would have been an issue for an RCD is two of them used earth as neutral.
    Other than that the only issue I've had is if I turn off my compressor at the GPO the RCD trips, though if I let it turn itself off or use the switch on the compressor its fine. I assume the compressor has a double pole switch, but have never looked into it.


    What brands of VSD cause nuisance tripping? I would like to be sure not to buy one.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Smart machines
    By neksmerj in forum METALWORK GENERAL
    Replies: 1
    Last Post: 3rd Jun 2016, 01:02 AM
  2. Levelling machines
    By Mike4 in forum METALWORK GENERAL
    Replies: 8
    Last Post: 5th Nov 2015, 09:26 AM
  3. Little Machines
    By kwijibo99 in forum METALWORK GENERAL
    Replies: 2
    Last Post: 23rd Jan 2015, 08:08 PM
  4. For Lovers of Old Machines
    By wheelinround in forum METALWORK GENERAL
    Replies: 3
    Last Post: 24th Dec 2012, 10:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •