Thread: testing 415 V motors
-
6th Jul 2018, 10:57 PM #1Senior Member
- Join Date
- Jul 2010
- Location
- Brisbane
- Posts
- 143
testing 415 V motors
I have several 415V 3 phase electric motors that I want to sell.. but It would be nice to see if they actually work first !..apart from plugging them in to someones factory, is there any other way to see if they are working ?
Ken
-
7th Jul 2018, 04:02 AM #2
Hi Ken,
As a first step, you will need a megger, is to check for any winding insulation breakdown to the case ! If they have an earth connection, check continuity to the metal frame. After checking that, then applying a three phase source to see if they run quietly without bearing rumbles. The three phase source could come from an inverter, single phase in, three phase out.Best Regards:
Baron J.
-
7th Jul 2018, 08:00 AM #3Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
As well as BJs recommendations the winding resistances should all be identical.
Even though they are 3P 415V they will still run on a 3P 240V VFD - they just won't develop full power.
-
7th Jul 2018, 05:36 PM #4
Thank you Bob, Yes I completely forgot to mention that. Sorry.
The only thing I would add is take extra care when measuring multi speed motors ! It is easy to make an error comparing multiple windings.Best Regards:
Baron J.
Similar Threads
-
Multiple motors from one VFD
By morrisman in forum METALWORK GENERALReplies: 16Last Post: 10th Jan 2016, 07:58 PM -
Treadmill Motors.
By j.ashburn in forum METALWORK GENERALReplies: 7Last Post: 24th Sep 2013, 08:22 AM -
CMG Motors
By GSRocket in forum METALWORK GENERALReplies: 17Last Post: 21st Aug 2012, 11:19 PM -
Swarf & Motors
By toolman49 in forum METALWORK GENERALReplies: 4Last Post: 28th May 2011, 11:01 PM