Thread: VFD Maintenance

  1. #1
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default VFD Maintenance

    I found this in the Powtran VFD manual and looks like useful info for folks with VFD in storage or on machine which have not been used for a while.

    Bottom line looks like ,that for VFDs that have not been run for between 1 and 2 years, the VFD needs to be left on for an hour or so before use under load.

    Beyond 2 years I'm not quite sire what " adjustable power" really means. It's the only section in the Manual that reads like "Chinglese" The rest I've read of the manual is very good.

    Caprecharge.jpg

  2. #2
    Join Date
    Nov 2007
    Location
    Near Rockhampton
    Posts
    270

    Default

    Quote Originally Posted by BobL View Post

    Beyond 2 years I'm not quite sire what " adjustable power" really means. It's the only section in the Manual that reads like "Chinglese" The rest I've read of the manual is very good.
    I presume they mean use an adjustable voltage source, probably a variac and increase the voltage in the recommended steps.

    John

  3. #3
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by GuzziJohn View Post
    I presume they mean use an adjustable voltage source, probably a variac and increase the voltage in the recommended steps.

    John
    Thanks John, it also looks like the charging current should be limited to 2A.

  4. #4
    Join Date
    Jul 2014
    Location
    Alphen aan den Rijn, Netherlands
    Posts
    208

    Default

    Quote Originally Posted by GuzziJohn View Post
    I presume they mean use an adjustable voltage source, probably a variac and increase the voltage in the recommended steps.

    John
    John,
    Yes, that it what I do exactly. I was told it has something to do with " regenerating the dielectricum" because "the capacitors dry out" or something. Maybe someone with real electrical knowledge can explain?

    Peter

  5. #5
    BobL is online now Member: Blue and white apron brigade
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    7,182

    Default

    Quote Originally Posted by WoodBee2 View Post
    John,
    Yes, that it what I do exactly. I was told it has something to do with " regenerating the dielectricum" because "the capacitors dry out" or something. Maybe someone with real electrical knowledge can explain?
    I did a bit of reading and this is one of the clearer explanations.
    The dielectric oxide layer is the thin high resistance layer that separates the two charge holding plates inside a cap.


    The dielectric oxide-insulating layer is created during manufacture. However, it will deteriorate in the absence of a sufficient rejuvenating voltage, and eventually the capacitor will fail if voltage is not applied. Maintaining the integrity of the dielectric requires the steady application of power. When voltage is applied, the oxide layer is rebuilt. The oxide layer thickness is the crucial factor to determine the voltage rating of the capacitor. Otherwise, the oxide layer will break down under voltage and cause a spectacular failure.By applying voltage to the capacitor on a regular basis, the oxide layer is “reformed”, and the integrity of the insulating characteristic is ensured. In EMA’s experience, the maximum time between power ups should be no longer than 1 year, provided the equipment is kept in a dry location at roughly 70 degrees F. Large temperature swings require less time between power ups.
    The procedure to “reform” the capacitors in electronic equipment is to apply rated voltage for a period of at least 1 hour. Realizing after the unit is de-energized, a chemical reaction is still occurring for up to 24 hours, thereby rebuilding the oxide layer during this “resting” period. Should more than 12 months pass between power ups, great caution should be exercised.

  6. #6
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    Something I can almost remember from my electronic engineering days!

    Yes, this relates to 'reforming' the dielectric.
    Reducing the input voltage means the leakage current is limited to a point which won't cause damage, while the reforming happens.

    The manual isn't the clearest in that part, for sure!

    This issue occurs with any gear with electrolytic caps.

    -russ

Similar Threads

  1. Electric Motor Maintenance
    By Geoff123 in forum METALWORK GENERAL
    Replies: 9
    Last Post: 27th May 2015, 10:04 AM
  2. Bridgeport 2J Maintenance
    By Bennett in forum METALWORK GENERAL
    Replies: 8
    Last Post: 31st Jul 2013, 05:01 PM
  3. Inverter Maintenance
    By citybook in forum WELDING
    Replies: 7
    Last Post: 2nd Feb 2012, 02:19 PM
  4. GMAW Course Lesson 5 - Maintenance .
    By Grahame Collins in forum WELDING
    Replies: 19
    Last Post: 23rd Feb 2009, 11:42 PM
  5. myford s7 maintenance
    By arkade31% in forum METALWORK GENERAL
    Replies: 10
    Last Post: 24th Oct 2007, 01:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •