    It's high time I sort out my vfd by adding a remote control panel.
    It's for a 6x26 mill. I'm looking for comments /suggestions as to what controls are useful, eg, reverse? Jog?. Run stop plus speed are obvious.
    And photos of actual panel layout would be great...
    Have you hard-wired it, or some type of connector?

    All thoughts welcome...



    -russ

  2. #2
    Join Date
    Aug 2010
    Location
    Near Bendigo, Victoria, AUS
    Age
    72
    Posts
    3,105

    Default

    Hi Russ,
    have a look at this thread: //metalworkforums.com/f65/t1838...n-huanyang-vfd
    They are my lathe and mill panels - and lots of discussion and discovery of VFD control parameters.
    I think I have the Huanyang ones down pat now
    As you can see, I like to have forward, reverse, for and rev jog, normal stop, emergency stop and table feeds, as well as a spindle rpm readout - all in the same panel. It works for me.
    Cheers, Joe
    retired - less energy, more time to contemplate projects and more shed time....

  3. #3
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    Thanks! A good read and something to consider.
    I had about decided jog wasn't necessary.

    -russ

  4. #4
    Join Date
    Aug 2010
    Location
    Near Bendigo, Victoria, AUS
    Age
    72
    Posts
    3,105

    Default

    You are absolutely righ: jog isn't necessary.
    However, I suspect it has saved me a couple of cutters so far: I'm clumsy at times and have been known to position a cutter too close to the work (like a corner of the workpiece between teeth or a misjuged reach of my flucutter). At my jog frequency of 5Hz, my motors produce very little torque - and the resulting "clunk" and a stopped spindle is all I got.... if you get my meaning.
    Cheers, Joe
    retired - less energy, more time to contemplate projects and more shed time....

  5. #5
    Join Date
    Mar 2017
    Location
    Virginia,USA
    Age
    34
    Posts
    1

    Default

    Hi...i am a new user here. I design electrical systems for industrial installations and I'm not clear on how to size a feeder for a control panel containing multiple VFD's. If I consider that control panel to be an Adjustable-Speed Drive System, 430.122 says Branch/Feeder conductors must be sized 125% of the input current of the power conversion equipment. Does that mean I need to add up the total VFD input current and add 25% for the feeder size?
    If I consider the control panel to be an Industrial Control Panel, 409.20 says the supply conductor must be sized for 125% of the full-load current of the largest motor plus the sum of the full-load current of all other motors. There's no mention here of VFD's or sizing the conductor based on VFD input current rather than motor full-load current.This gets to be an issue where a panel shop puts several over-sized drives in a panel. I recently had a project where there were 15 VFD's in a panel serving 1HP - 5HP motors, and the shop put in all 7.5HP drives.

  6. #6
    Join Date
    Oct 2015
    Location
    melbourne
    Posts
    473

    Default

    It appears you are quoting USA codes? Presumably you are in the USA. Id suggest you consult a local qualified engineer, perhaps also your inspector, as it seems to me the definition of the type of panel is the critical issue here, and that may partially at least a matter of local practice.

    -russ

  7. #7
    Join Date
    Jul 2006
    Location
    Athelstone, SA 5076
    Posts
    4,258

    Default

    Quote Originally Posted by HattyDamp View Post
    Hi...i am a new user here. I design electrical systems for industrial installations and I'm not clear on how to size a feeder for a control panel containing multiple VFD's. If I consider that control panel to be an Adjustable-Speed Drive System, 430.122 says Branch/Feeder conductors must be sized 125% of the input current of the power conversion equipment. Does that mean I need to add up the total VFD input current and add 25% for the feeder size?
    If I consider the control panel to be an Industrial Control Panel, 409.20 says the supply conductor must be sized for 125% of the full-load current of the largest motor plus the sum of the full-load current of all other motors. There's no mention here of VFD's or sizing the conductor based on VFD input current rather than motor full-load current.This gets to be an issue where a panel shop puts several over-sized drives in a panel. I recently had a project where there were 15 VFD's in a panel serving 1HP - 5HP motors, and the shop put in all 7.5HP drives.

    i cant help wonder as to how and why you can design such electrical systems and yet ask for said info on a public forum which WILL contain non qualified advice.

  8. #8
    Join Date
    Sep 2012
    Location
    York, North Yorkshire UK
    Posts
    6,477

    Default

    Quote Originally Posted by HattyDamp View Post
    Hi...i am a new user here. I design electrical systems for industrial installations and I'm not clear on how to size a feeder for a control panel containing multiple VFD's. If I consider that control panel to be an Adjustable-Speed Drive System, 430.122 says Branch/Feeder conductors must be sized 125% of the input current of the power conversion equipment. Does that mean I need to add up the total VFD input current and add 25% for the feeder size?
    If I consider the control panel to be an Industrial Control Panel, 409.20 says the supply conductor must be sized for 125% of the full-load current of the largest motor plus the sum of the full-load current of all other motors. There's no mention here of VFD's or sizing the conductor based on VFD input current rather than motor full-load current.This gets to be an issue where a panel shop puts several over-sized drives in a panel. I recently had a project where there were 15 VFD's in a panel serving 1HP - 5HP motors, and the shop put in all 7.5HP drives.
    Both are correct ! In essence what it is saying is that the feeder has to be sized according to the biggest load, that is the sum of all the loads plus 25%. The fact that you have an installation that has oversized VFD's driving undersized loads is not the issue. The total load is.

    As far as VFD's are concerned it is probably cheaper to buy all 7.5HP units than to buy different sized ones to suit each load. In terms of inventory it would be less costly managing only one size than having to manage a dozen.
    Best Regards:
    Baron J.

Similar Threads

  1. Milling machine control panel issue
    By oohsam in forum METALWORK GENERAL
    Replies: 33
    Last Post: 23rd Dec 2016, 08:13 PM
  2. VSD Remote Control Panel Questions
    By markjaffa in forum METALWORK GENERAL
    Replies: 28
    Last Post: 20th Apr 2010, 05:15 PM
  3. remake panel
    By jackaroo in forum METALWORK GENERAL
    Replies: 10
    Last Post: 11th May 2008, 10:07 PM
  4. 7 x14 control panel puzzle?
    By Malfie in forum METALWORK GENERAL
    Replies: 3
    Last Post: 11th Jul 2007, 11:35 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •