28th Jun 2015, 06:26 PM #16Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
bwah, the VFD must not have a switch between it and the motor connections as the VFD must do the switching otherwise you will damage both the VFD and the motor.
While the motor is running the VFD MUST not be disconnected from the motor.
My guess is it will be something like in the following picture BUT lets get confirmation from at least one other source
forget about your blue L3, L2 and L1 labelled terminals they will no longer be able to be used because they connect to a switch underneath through to my green labelled L3, L2 and L1 labelled terminals.
The VFD has to be connected to my green L3, L2 and L1 labelled terminals.
Currently you will find metal strips between my green L3, L2 and L1 labelled terminals.
These have to be removed and placed in the orientation I have shown by the green loops in the picture.
Let me stress again that we need more confirmation before you connect up anything.
-
28th Jun 2015, 06:42 PM #17Most Valued Member
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 9,088
I think you're barking up the wrong tree Bob. Don't you need 6 wires to be able to change from star to delta?
I've no idea what the links are for.......... maybe for a motor that has the star point bought out to the switch terminals?
Stuart
-
28th Jun 2015, 06:42 PM #18Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
benhoskin, the red wires from the switch go into the motor housing.
there is no other terminal accessed externally on the motor.
access to red wires would require access into motor housing.
IMG_2178.jpgIMG_2177.jpg
-
28th Jun 2015, 06:57 PM #19Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
hi bob,
'assuming' the input wires (cyan coloured L1,L2,L3) are connected to the switch.
if they were removed and placed to the green L1,L2,L3 terminals and the metal strips were rearranged to match a delta arrangement (pictured),
this would essentially be a 'standard' connection bypassing the switch?
delta1.JPG
-
28th Jun 2015, 07:13 PM #20Golden Member
- Join Date
- Sep 2008
- Location
- Riddells Creek, Vic.
- Posts
- 838
The motor appears to be "Star" only despite what is written on the name plate. The switch may have NO/NC and common terminals.
-
28th Jun 2015, 07:41 PM #21Diamond Member
- Join Date
- Jun 2010
- Location
- Canberra
- Posts
- 1,322
It appears that switch was designed to have 3 more leads going to it, the bridged terminals forming the centre of the star, in which case they could have been re-arranged to delta.
I'm wondering if that motor's been rewound and they decided not to bother bringing out the other ends of the windings?
-
28th Jun 2015, 08:20 PM #22Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
based on the last two posts, does this mean the motor in its current state is not suitable for 240v output?
if this is the case what would be required to enable this to occur?
thanks
Ben
-
28th Jun 2015, 08:46 PM #23Most Valued Member
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 9,088
-
28th Jun 2015, 09:10 PM #24Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Correct - forgot about that.
Ben forget everything I have written up until now.
I'm wondering if that motor's been rewound and they decided not to bother bringing out the other ends of the windings?
Ben that motor cannot be converted to delta at the junction box - it needs 6 wires (not 3) coming from the motor to reconfigure between ∆ and Y.
The common point inside the windings needs to be dug out and broken into 3 separate leads. Each of these leads then needs to be brought outside the motor and connected to an appropriate one of those red wires coming from the motor.
This is not a job for the faint hearted best to take it to a motor rewinder and get then
-
28th Jun 2015, 10:26 PM #25Intermediate Member
- Join Date
- Aug 2008
- Location
- Perth
- Posts
- 26
Now that we have seen the motor terminal box, you will have to do as Bob suggests,
if you want full motor hp either dig out the star point or take it to a motor rewinder to do it for you.
If you can live with 1/2 of the stated motor hp then you can wire it as is.
-
28th Jun 2015, 11:23 PM #26Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
thanks for everyones input, very helpful
i will investigate having it re-wired in delta
keep u posted
-
2nd Jul 2015, 07:48 PM #27Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
bingo! wires have now been brought out and connected in delta. see image below
If this is the case, can i leave the switch in the 'on' position and only turn the motor on via the VFD?
Delta220v.jpg
-
2nd Jul 2015, 08:28 PM #28Member: Blue and white apron brigade
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 7,189
Great - did you do this yourself?
If this is the case, can i leave the switch in the 'on' position and only turn the motor on via the VFD?
OR
Even if it's off but someone sees it as "on" and turns it of fand you then turn on the VFD - not good.
I would just wire the switch permanently on by moving the wires as shown
So each phase will have 3 wires attached to each other,
Delta220vx.jpg
Or At least gaffer tape cover the switch in the on position.
-
2nd Jul 2015, 08:56 PM #29Novice
- Join Date
- Oct 2014
- Location
- SA
- Posts
- 20
ok thanks again bob
and no i didnt bring the wires out.. i left that job for local motor rewinder
cheers
-
3rd Jul 2015, 12:40 AM #30Most Valued Member
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 9,088
If space permits I'd think about adding a terminal block to directly connect the VSD to the windings, leaving the switch free to switch the VSD.
Stuart