    Hi Guy's,
    Was curious if any of you have had good success in using a non inverter arc welder on a non inverter gen set?
    I tried a few different arc welders on a 8KVA Honda powered gen set, but overall a poor result I thought.
    Arc hard to start and would cut out, even sound and look not the same as grid supply.
    From the results I would assume it was doing the gen set no favours also.
    Live and learn.
    Trev

  2. #2
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    6,216

    Default

    8kva should be plenty to run a small ~140 amp transformer single phase stick welder.

    We used to run them on 5kva dunlites.
    Gold, the colour of choice for the discerning person.

  3. #3
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    The welder runs but it's a different machine on the grid.

  4. #4
    Join Date
    Sep 2010
    Location
    Lebrina
    Posts
    1,910

    Default

    Quote Originally Posted by TrevTronic View Post
    The welder runs but it's a different machine on the grid.
    You are dead right. I have done a fair bit of welding off generators with transformer machines and my observations have been that the quality of the gennie makes a difference, the quality of the welder also has a large bearing, arc starting will be harder and they do not perform as well as there simply isn't the reserve capacity in a generator that the grid has. I generally stuck to 2.5mm electrodes where possible unless I had a really good generator and welder. It pays to remember that momentary spikes in primary current can be as high as 90 odd Amps when running 100 Amps welding current with a transformer machine and that takes a lot of gennie and a fast reacting governor and voltage regulator to handle.

  5. #5
    Join Date
    Jun 2010
    Location
    Canberra
    Posts
    1,322

    Default

    Might be worth trying an inverter welder? The 140 amp units are pretty cheap.

    I was able to run a 2.5mm rod at around 60-70 amps off a cheap-arsed Bunnings 2kVA genny, although I had to try a few times to get a very "gentle" arc start otherwise the breaker would trip.

  6. #6
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    Thanks Karl,
    The spikes would also be killing the gennie.
    When you mention a really good gen set, is that a pure sine wave gen set or just a really big output one?

  7. #7
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    Hi Rusty,
    I read that most cheap entry level inverter welders do not like any power source other then pure sine wave.
    The more expensive ones come with generator safe ratings.

  8. #8
    Join Date
    Jun 2010
    Location
    Canberra
    Posts
    1,322

    Default

    Quote Originally Posted by TrevTronic View Post
    Hi Rusty,
    I read that most cheap entry level inverter welders do not like any power source other then pure sine wave.
    The more expensive ones come with generator safe ratings.
    I'd expect all generators to put out a sine wave as that's the way they make power. What may vary between generators is the quality of the voltage regulation.

    As for cheap inverters, the one I used is a BOC Smootharc 130, which was about $300 when I got it a decade or more ago, and is probably even cheaper these days.

  9. #9
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    Quote Originally Posted by RustyArc View Post
    I'd expect all generators to put out a sine wave as that's the way they make power. What may vary between generators is the quality of the voltage regulation.

    As for cheap inverters, the one I used is a BOC Smootharc 130, which was about $300 when I got it a decade or more ago, and is probably even cheaper these days.
    Pure sine wave is what is required to run certain electronics such as laptops etc
    But many inverter welders also need Pure sine wave to work correctly and to have a long life, for example many of the cheap inverter welders on ebay are not recommended to run on generators other then Pure sine wave generators, I have asked a few sellers this question.
    Higher end models will state generator compatible.

  10. #10
    Join Date
    Sep 2010
    Location
    Lebrina
    Posts
    1,910

    Default

    Quote Originally Posted by TrevTronic View Post
    Thanks Karl,
    The spikes would also be killing the gennie.
    When you mention a really good gen set, is that a pure sine wave gen set or just a really big output one?
    By really good, I primarily meant big output, but quality also plays a part.
    Some gensets use chopped DC, although in thinking about it, most of these have been attached to lower end mobile welders, so that negates the need to run a transformer arc welder from them, although power tools are pretty gutless when run on a chopped DC supply.
    Not all inverters are created equal though and some have running issues and others short lives when run on the type of gensets that we commonly see.
    The gensets we use in the field really are only designed for somewhat intermittent usage, which is fair enough. If one compares the alternator unit from a typical 8Kva unit with that found on a Kubota backup genset for example, the differences are easy to see. The backup genset alternator is almost twice the size and is run by a twin cylinder diesel, liquid cooled engine and is designed to output 8Kva continuously for long periods. Likewise, the cost of the backup genset reflects this greater performance, plus you'd need a forklift to move it.
    I think the bottom line is that inverters are a vast improvement over transformer machines in just about every way, however a transformer unit can be run effectively as needs require. If I was doing a lot of site work, I'd still pick my Perkins powered Lincoln over any genset powered unit. Next would be my Lincoln Invertec 170, then finally, my WIA 12P SCR controlled transformer machine, (this machine welded an awful lot of irrigation pipes off a 5Kva Dunlite).

  11. #11
    Join Date
    Jun 2010
    Location
    Canberra
    Posts
    1,322

    Default

    Quote Originally Posted by TrevTronic View Post
    Pure sine wave is what is required to run certain electronics such as laptops etc
    But many inverter welders also need Pure sine wave to work correctly and to have a long life, for example many of the cheap inverter welders on ebay are not recommended to run on generators other then Pure sine wave generators, I have asked a few sellers this question.
    Higher end models will state generator compatible.
    I should have said I was referring to non-inverter generators, which no matter how cheap, still produce a perfect sine wave. I've never used an inverter-style generator, so can't really comment on them.

    It's worth noting that a laptop power supply and an inverter welder are pretty much the same thing - a switchmode power supply, although the former is designed to put out a constant voltage, while the latter is set up for constant current.

    As for compatibility with inverter generators, I'm going to guess that the peak voltages and harmonics from a modified sine wave inverter are tough on the input capacitors, leading to premature failure if they're not specced high enough, and may well pose challenges for the regulation circuitry, leading to poor welding behaviour.

  12. #12
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    Quote Originally Posted by Karl Robbers View Post
    By really good, I primarily meant big output, but quality also plays a part.
    Some gensets use chopped DC, although in thinking about it, most of these have been attached to lower end mobile welders, so that negates the need to run a transformer arc welder from them, although power tools are pretty gutless when run on a chopped DC supply.
    Not all inverters are created equal though and some have running issues and others short lives when run on the type of gensets that we commonly see.
    The gensets we use in the field really are only designed for somewhat intermittent usage, which is fair enough. If one compares the alternator unit from a typical 8Kva unit with that found on a Kubota backup genset for example, the differences are easy to see. The backup genset alternator is almost twice the size and is run by a twin cylinder diesel, liquid cooled engine and is designed to output 8Kva continuously for long periods. Likewise, the cost of the backup genset reflects this greater performance, plus you'd need a forklift to move it.
    I think the bottom line is that inverters are a vast improvement over transformer machines in just about every way, however a transformer unit can be run effectively as needs require. If I was doing a lot of site work, I'd still pick my Perkins powered Lincoln over any genset powered unit. Next would be my Lincoln Invertec 170, then finally, my WIA 12P SCR controlled transformer machine, (this machine welded an awful lot of irrigation pipes off a 5Kva Dunlite).
    Thanks for all the info and I think you hit the nail on the head with with your Perkins powered Lincoln, maybe not that big for me but an engine driven alternator welder would appear the best off the grid choice.

  13. #13
    Join Date
    Jul 2018
    Location
    Black hill South Australia
    Posts
    19

    Default

    Quote Originally Posted by RustyArc View Post
    I should have said I was referring to non-inverter generators, which no matter how cheap, still produce a perfect sine wave. I've never used an inverter-style generator, so can't really comment on them.

    It's worth noting that a laptop power supply and an inverter welder are pretty much the same thing - a switchmode power supply, although the former is designed to put out a constant voltage, while the latter is set up for constant current.

    As for compatibility with inverter generators, I'm going to guess that the peak voltages and harmonics from a modified sine wave inverter are tough on the input capacitors, leading to premature failure if they're not specced high enough, and may well pose challenges for the regulation circuitry, leading to poor welding behaviour.
    Thanks for your feedback.

Similar Threads

  1. TIG welding SS
    By Michael G in forum WELDING
    Replies: 53
    Last Post: 7th Apr 2017, 07:40 AM
  2. Welding through POR 15
    By simso in forum WELDING
    Replies: 3
    Last Post: 18th Oct 2016, 08:37 PM
  3. Where do you do your welding?
    By jmk89 in forum METALWORK GENERAL
    Replies: 16
    Last Post: 13th Mar 2008, 01:42 AM
  4. new to welding.
    By Bluegum in forum WELDING
    Replies: 8
    Last Post: 24th Oct 2006, 09:22 PM
  5. welding tip
    By mako in forum WELDING
    Replies: 4
    Last Post: 7th Jul 2006, 04:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •